Hello everyone!

Since the cold weather started I’ve noticed that the Programer (Honeywell ST9420C) isn’t working properly.
It doesn’t turn on/off in the auto pre set times in the C/H mode. It works correctly in the auto pre set times in the H/W mode. The C/H is effectively on constantly, turning on/off on the thermostat.
I have a Honeywell DTS92E1020 RF stat, I’m guessing it’s paired correctly with the programmer because it does turn the heating on/off when the temperature drops/rises or is adjusted.

Any ideas why the auto times in C/H mode aren’t having any effect?
 
Hello everyone, thanks for getting back to me so quickly.

The heating was coming on if the temp in the house dropped below the temp set on the RF room stat. This was happening even if the programmer was in the AUTO (OFF) part of the days timer settings. Hope that makes sense!!

Since “resetting”/changing the times (only by 10 minutes here & there) on the C/H pre set daily on/off times, the problem has rectified!!
It seems like changing/resetting the times has rebooted the programmers C/H timer. Like the programmer didn’t log the previous set of installed times. That’s the only way I can explain the sudden change.

Anyway, worth remembering if there’s a similar problem with one of these or maybe any programmers. Try putting the times into the programmer again! Worked for me!!

Cheers, everyone 👍
 

Reply to Honeywell Controls Fault? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
292
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
423
  • Question
Hi Wondering if anyone could point me in the right direction please. We have an old traditional old Potterton E50 boiler with an old Honeywell...
Replies
1
Views
672
Deleted member 120897
D
So I've used a wireless thermostat to activate my heating since installation, but it's just stopped working (Blank screen, no new battery's fixed...
Replies
0
Views
2K
Hello everyone, I'm facing an issue with my Vaillant EcoTec 832 boiler and would greatly appreciate your expert advice. The Problem: Heating...
Replies
8
Views
989
Back
Top