I have an old Hydra Daryl integrated screen & shower. Unfortunately it’s leaking in the column through into my kitchen ceiling! I’ve had a plumber round to try & see what’s wrong but he couldn’t get into the column!! There is only 1 grub screw on one of the controls but it seems that front part of the column should come off. Anyone know how to get into it? Many thanks
 
I have similar problem with my Daryl Hydracadia shower. I can't get into the column or remove the cartridges. Showerdoc say they might have spare parts but want me to remove cartridges to show them. I can't find any grub screws. Did you ever find the solution?
 
I have a similar shower. Daryl Hydracadia corner column. Also leaking if not on "head " setting and temp and flow valves not working. Showerdoc say they might have spare parts but I need to remove cartridges or open up column to show them. I can't find any grub screws ...can you help. Did you find out how to open up the column?
 

Attachments

  • 16535596152518398555991341515755.jpg
    16535596152518398555991341515755.jpg
    384.7 KB · Views: 22
  • 16535596285457594833032937257160.jpg
    16535596285457594833032937257160.jpg
    324.3 KB · Views: 22
  • 16535596551664925381173140768808.jpg
    16535596551664925381173140768808.jpg
    411.6 KB · Views: 25
Wondering if the indice in the centre of the contol and temp valves either unscrew or pop out much like those on a bath/ basin tap can.
 
I have a similar shower. Daryl Hydracadia corner column. Also leaking if not on "head " setting and temp and flow valves not working. Showerdoc say they might have spare parts but I need to remove cartridges or open up column to show them. I can't find any grub screws ...can you help. Did you find out how to open up the column?

You cannot gain access from the front.
Remove the black cap at the top of the column and look down inside, you will see a laser cut ‘W’ bracket with 4 short screws. Remove the screws and then pull the complete column forward from the top and it will unclip. You can then disconnect the push fit pipes and then remove the column completely. On the back you then disconnect the various pipes and make a note of the current settings on the controls on the front. Then remove the 4 securing screws holding the flow/temp/diverter assembly and pull the complete assembly out. Replace any parts you need to, you may will have difficulty sourcing them!

Reverse the above to reinstall making sure the controls all line up in the same place as when you removed them. You may well find that some of the 10mm push fittings leak when you reinstall it so best to have some spares.

The above is quite complex, take photos as you go along. If you struggle to get hold of the parts you need send me a message as I may be able to help.
 
You cannot gain access from the front.
Remove the black cap at the top of the column and look down inside, you will see a laser cut ‘W’ bracket with 4 short screws. Remove the screws and then pull the complete column forward from the top and it will unclip. You can then disconnect the push fit pipes and then remove the column completely. On the back you then disconnect the various pipes and make a note of the current settings on the controls on the front. Then remove the 4 securing screws holding the flow/temp/diverter assembly and pull the complete assembly out. Replace any parts you need to, you may will have difficulty sourcing them!

Reverse the above to reinstall making sure the controls all line up in the same place as when you removed them. You may well find that some of the 10mm push fittings leak when you reinstall it so best to have some spares.

The above is quite complex, take photos as you go along. If you struggle to get hold of the parts you need send me a message as I may be able to help.
Thanks, your advice was 100 percent correct and actually pretty straightforward. I found 3 problems. 1 of the push fit pipes was leaking. That's an easy fix. The 2 main problems were worn and broken plastic temp spline 204292. And plastic flow spline 200342. I found a place to buy the flow spline. But the temp spline 204292 is discontinued and I can't find online. Can you help find 1?
 
You cannot gain access from the front.
Remove the black cap at the top of the column and look down inside, you will see a laser cut ‘W’ bracket with 4 short screws. Remove the screws and then pull the complete column forward from the top and it will unclip. You can then disconnect the push fit pipes and then remove the column completely. On the back you then disconnect the various pipes and make a note of the current settings on the controls on the front. Then remove the 4 securing screws holding the flow/temp/diverter assembly and pull the complete assembly out. Replace any parts you need to, you may will have difficulty sourcing them!

Reverse the above to reinstall making sure the controls all line up in the same place as when you removed them. You may well find that some of the 10mm push fittings leak when you reinstall it so best to have some spares.

The above is quite complex, take photos as you go along. If you struggle to get hold of the parts you need send me a message as I may be able to help.
HI - newbie here...
I have the Daryl Hydra and the flow diverter is stuck on the foot setting, the lever moves but doesn't adjust the water flow. Is there and way remove the lever and enclosure and set it to the "head" flow and leave it at that, without taking the column apart which sounds like it might open another can of worms with leaks etc. I have removed the grub screw from underneath the domed fitting but not sure what should come apart from that or how, and don't want to mark the chrome with wrench's if nothing is meant to come apart. Any ideas gratefully received
 
HI - newbie here...
I have the Daryl Hydra and the flow diverter is stuck on the foot setting, the lever moves but doesn't adjust the water flow. Is there and way remove the lever and enclosure and set it to the "head" flow and leave it at that, without taking the column apart which sounds like it might open another can of worms with leaks etc. I have removed the grub screw from underneath the domed fitting but not sure what should come apart from that or how, and don't want to mark the chrome with wrench's if nothing is meant to come apart. Any ideas gratefully received

The dome comes off with a quarter turn. The plastic spline behind it will be split due to age so will just spin when selecting head/feet/hose. Twist spline to head with pliers. Then Glue repair plastic spline them resemble in reverse. Don’t move selector again if poss. Replacements are very difficult to find
 

Reply to How do you get into the column of a Daryl Hydra shower? in the USA area at PlumbersForums.net

Similar plumbing topics

I have a Daryl Hydracadia corner shower column. It has 3 problems that all developed nearly at the same time. It leaks when not on "head" setting...
Replies
1
Views
1K
Hi I have a Hydra Classic 414 shower column. The spine to the flow control snapped. I have got a replacement spine from shower spares but now...
Replies
0
Views
414
Hi - hope you can help. The on/off tap (part number 204543) on my Daryl Hydra classic shower has broken inside. I spoke to Kohler UK but they...
Replies
7
Views
2K
I have a ceiling fitted shower that keeps dripping and is driving me crazy. Can anyone offer any guidance to what’s causing the problem and how it...
Replies
6
Views
2K
I’m trying to fix a leaking tap in my kitchen. I’ve located where the grub screw should be but it’s just an empty hole. I’m looking at it with a...
Replies
4
Views
1K
Aquarius
A
Back
Top