Hi all,
My customer has a gatevalve/bypass off the primary flow into his cylinder.
He has fiddled with it (I think he was trying to turn off the water, and got the wrong valve).
How best to set it up?
I'll have to check to see if the system is on a three-port or two-port valves (if it's relevant).
Thanks all,
Jennie
IMG_0271.JPG
 
Hi Jennie,
This is an ‘old school’ method of regulating the
flow of water through the cylinder heat exchanger
(Coil) although usually fitted on primary return.
The idea is by reducing the flow, the coil will remain hotter longer. Thus heating the water quicker.
Nothing to do with modern pressure differential by-passes.
So the answer you seek, is by trial and error.
Crank it about two full turns from fully open and see how it goes.
 
Hi Jennie,
This is an ‘old school’ method of regulating the
flow of water through the cylinder heat exchanger
(Coil) although usually fitted on primary return.
The idea is by reducing the flow, the coil will remain hotter longer. Thus heating the water quicker.
Nothing to do with modern pressure differential by-passes.
So the answer you seek, is by trial and error.
Crank it about two full turns from fully open and see how it goes.
Given the position of the gate valve it's clearly acting as a bypass and in no way will affect the flow rate of water through the cylinder coil. I'd agree with Riley with fitting an auto bypass but would first check whether it's actually required. If the system is on a 3 way valve then I would just remove it.
 
In the photo, you can’t make out where it’s teed from.
I assumed it was directly from either a zone or mid-position valve. However, after reading your reply Craig and looking at the photo again.
I now feel you are right and I’m mistaken
It does look too low down to be the flow??
 
Yeah the photo looks to me like it's at the base of the cylinder and the gate valve is is tee'd into the top of the cylinder return pipe
 
Hi all,

Thanks so much for your comments. I'll have to go back and check out the surrounding pipework/zone valves/etc.

I'm a bit confused about the three-way valve versus the two zone valves. Surely both shut water off to the hot water and central heating circuits. So why isn't a bypass needed on the three way valve?
 
Hi all,

Thanks so much for your comments. I'll have to go back and check out the surrounding pipework/zone valves/etc.

I'm a bit confused about the three-way valve versus the two zone valves. Surely both shut water off to the hot water and central heating circuits. So why isn't a bypass needed on the three way valve?
A 3 port valve always keeps a circuit open so a bypass isn't required
 

Reply to how to set bypass (the old, red gate valve type) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below...
Replies
3
Views
733
  • Question
Central Heating Pump - G Pump Force HE-RS25/6PWM-130 Hi, I would be grateful if someone could explain whether our CH system can cope with the...
Replies
7
Views
631
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
Hi everyone, Is this set up correct: Attic stop valve turns off the cold water to my bathroom (I think it is the rising main in the attic which...
Replies
0
Views
539
Hi, we had UFH installed dowstairs in our house recently, and I'm not 100% sure that it's connected correctly. I'd be grateful if someone could...
Replies
7
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock