Hi..so the Baxi combi at my folks' house has lost pressure twice over a period of a couple of weeks since they started using the central heating this winter....but each time it's happened there's no air build up to be bled from any of the radiators.
Am I right in thinking that the pressure drop is a boiler issue and not a pipework/radiator leak?
Thanks in advance.
 
ok, make sure its at 1 bar now run your heating on full and wait and watch the presure on the boiler, does it go up to or near 3 bar, this may take some time, if it does then it means your expantion vessel needs recharge.
 

Reply to Loosing pressure but no air in rads in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed...
Replies
1
Views
265
When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like...
Replies
35
Views
1K
Hi - I'm a reasonably experienced DIY plumber but just can't work out why the last new rad I've installed is cold - would really appreciate your...
Replies
7
Views
669
M
Hi, we have a back combi heater. Whenever the heating comes on it seems to lose pressure within a few hours and I have to refill each morning...
Replies
1
Views
407
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
606
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock