I have installed a system and am only getting a 6degree difference between the flow and return. I have knuckled the locksheilds down on the rads closest the boiler and also lowered the pump speed. To increase it all that can be done is to knuckle the locksheilds down further? Though this is just about stopping enough heat getting too the rads. Thanks.
 
Sounds like the rooms are upto temperature?
 
Suggesting the delta t maybe higher when the rooms are still trying to get to temperature?

correct you will get a lower delta when the rooms are upto temperature
 
Are you measuring this deltaT at the boiler? if so, maybe by pass open.
If your boiler is still running (and not cycling) at 12kw then the flowrate is 28.7 LPM (1.72M3/hr) @ deltaT of 6C which seems extremely high from a pump on reduced speed, I would think most systems would circulate at ~ 1 M3/hr (max) which gives a deltaT of 10.3C @ 12kw.
If the boiler is cycling then you can get a small deltaT but with a fairly low boiler flow temp of maybe 40/45C. resulting in a low rad/boiler output.
 