Hi can anybody help me with a problem I am having.
following a power cut the heating and hot water failed. The boiler would light but it would go out because of no flow. I thought it was the programmer blown because if it wasn’t calling for heat or hot water it doesn’t trip the electric,but as soon as it calls it blows the trip controlling the megaflow. The pump and both the 2 ports are not working, but the element is heating the water. The problem is that the boiler is not . The boiler is a Worcester 12 ri and is brand new the programmer was changed for a new one with the same result.the boiler is upstairs and the megaflo is in garage andthe Power for the megaflo is from an rcd which then goes to a fused spur and from there into the megaflo. Does anybody have any ideas.
 
does the pump have power ?
 
Ok picture of the mega flow please
 
We had a leaking diverter valve, thats the first thing I'd be checking for if its tripping the power, especially if its an RCD or RCBO. Make sure the power is definitely isolated before poking around in there though. Might be best handled by a professional.
 
We had a leaking diverter valve, thats the first thing I'd be checking for if its tripping the power, especially if its an RCD or RCBO. Make sure the power is definitely isolated before poking around in there though. Might be best handled by a professional.
Done a few tests, the pump does work , but I have to manually trigger the micro switch to get the pump to run,if I pull the override lever the pump starts momentarily,but won’t run .when I took the cover of the valve and opened it fully and kept it there it would run for as long as I held it open.when I put the multimeter on the wires from the programmer(water and heating) I am only getting 13 volts
 
Are these supposed to be at mains voltage or could 13 volts be correct? I heard a fizzing noise from the diverter valve in our main combi boiler. Seems daft that 240 volts could be right next to something that could leak like that valve.
Strange too that it didn't blow the 13 amp fuse on the boiler. Guess water isn't as good a conductor as copper but still glad I didn't touch it...
 

Reply to Megaflo system fit not working in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
277
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
127
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323