motorized valve- jammed on microswitch

went to a call today where customer complained about pump running constantly even when programmer in off position & room stat / cylinder stat turned down. s plan system & both zone valve motors where turning ok. orange wire to pump & boiler was permanently live due to htg zone valve microswitch jammed in on position. i dont do a great deal of fault finding work, mainly new installs. just wondered how common a fault this is as most zone valve problems ive seen are usually burnt out motors.
 
Last edited:
It's a common one that throws a lot of guys/galls into thinking the programmer or room stat is faulty! It can be any of the zone valves that give this fault. Process of elimination gets you to the one at fault though :)
 
Always happening, even on motorised valves only a year or two old. Seems the actual mechanical bits of the valves don't get a chance to wear out!
 
Easiest way of tracking this is to just disconnect the (zone valve) orange wires one at a time from the 10 way, when it stops you know which valve is causing the problem.

And yes it is quite common as well as jammed motors.
 
Motorised valves are a pain, my advice is to replace the complete valve ( head and body) if faulty, been fitting a type of motorised valve ( I think seimens) that has a plug into the valve head, a lot easier to change than 6 poxy wires. Jon
 
I have a system with a three way Drayton motorised valve, every three to four years the actuator packs in (I think the heat in the airing cupboard slowly toasts the micro switches). I now keep a spare ready to fit. The actuator can be changed in about 5 minutes as it just clips onto the valve body. Very common fault I think, but can be confusing to diagnose unless you've seen it before!
 
Status
Not open for further replies.

Reply to motorized valve- jammed open microswitch in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Customer complains of Intermittent heating on Y plan with Stat satisfied. New boiler fitted last year (no permanent live required or fitted...
Replies
25
Views
2K
Hi guys, I have a fault on a clients heating system whereby the heating will stay on regardless of what the programmer is doing on its timed...
Replies
14
Views
2K
    • Like
Hi all, We recently purchased a house and nothing seems to work correctly here, I've spent weeks rectifying issues. Plumbing, electrical...
Replies
47
Views
5K
P
Hi there, please help dont have a clue how to set this up. Ive recently installed a complete new central heating system in my house myself. The...
Replies
22
Views
4K
Hi all Just seeing if this is a common method of providing a boiler bypass thesedays as there seems so many ideas out there, years ago if we...
Replies
22
Views
5K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock