Messages
15
New double panel column radiator

Cold

Turned off all rads not helped

Checked trv pin seems fine

Locksheild i think is ok see pic sttached

Its new so didnt need to flush

Cant really balance because the only thing that is hot is the copper pipes

So instructions came with it about how it flows or something i chose option 5 both my trv and lockshield are at the bottom someoje said one trv should he at top and one at bottom but iv never seen a rad with valves one up and one down

See pics
 

Attachments

  • E73AF09D-849E-4412-AA42-9EED2D6D6B14.jpeg
    E73AF09D-849E-4412-AA42-9EED2D6D6B14.jpeg
    384.7 KB · Views: 24
  • 9F0473B8-B915-472C-B74C-C137F66A33B7.jpeg
    9F0473B8-B915-472C-B74C-C137F66A33B7.jpeg
    469.8 KB · Views: 20
  • 33CF2C32-12FA-4C7B-A70D-897441459775.jpeg
    33CF2C32-12FA-4C7B-A70D-897441459775.jpeg
    441.9 KB · Views: 22
  • ADF9F1B5-27E6-4A76-A45B-DF8385EA1E29.jpeg
    ADF9F1B5-27E6-4A76-A45B-DF8385EA1E29.jpeg
    366.2 KB · Views: 22
  • 53827C32-E311-4739-84A4-84651D3957EE.jpeg
    53827C32-E311-4739-84A4-84651D3957EE.jpeg
    329 KB · Views: 21
  • 76B7ED2A-8919-4369-A5AB-EBEF4A186CA2.jpeg
    76B7ED2A-8919-4369-A5AB-EBEF4A186CA2.jpeg
    389 KB · Views: 19
  • 634E4BE2-4827-4182-8300-0346D83F49D6.jpeg
    634E4BE2-4827-4182-8300-0346D83F49D6.jpeg
    468.7 KB · Views: 22
Is the lockshield fully open?

Was there a radiator in that location before and if so did that work O.K?
If so was it smaller / larger / similar sized a the new one?
Where do the flow and return pipes originate

Could that radiator be mounted either way up, was there a sticker indicating Top /Bottom?
If there is a baffle in one of the headers it may have ended up at the top instead of the bottom although looking at the drawings I think they would have marked the baffle on there if there was one.

It should work flow and return in the bottom, if it did need to be top / Bottom there would have been a label on the radiator.
 
Last edited:
Is the bottom of the rad hot ?
 
And if you turn all the other trvs off on the rads it doesn’t get hot / any hotter
 
The product sheet says "When we place the order we will enter the ERP for the upper and lower", what does this mean.

Mabe shut both valves, remove the vent and then prove flow by alternatively opening/shutting valves.
 
No, on the top of the rad at one or both ends you should see blank plugs one of which should have a vent/bleed screw that you can open/remove with a screwdriver or a key.
Slacken this after shutting both valves, then remove it completely, put a dish/bucket under it and then open say the TRV fully first and you should get a good flow of water, shut the TRV then do likewise with the Lockshield valve.

1671283143049.png
 
Ok i did bleed it only water cameout

Ill try this lastthin
So

Where u bleed it take that whole part off from
The radiator then turn on the trv open it

Let watwr come out


Then go on other side take the bleed valve out that side and open lsv so water comes out

Generally what is this doing? Because it has got water in it
 

Reply to New column rad cold devastated in the UK Plumbers Forums area at PlumbersForums.net