Are you referring to the photo in post#12?, I see 6&10 and 8&10 linked there, I also see 2 orange wires going to terminal 9?. If you have a Mmeter you can see very quickly if the orange wire(s) terminal has 230V when the zone valves are switched, also where is the boiler circ pump fed from?.
 
Are you referring to the photo in post#12?, I see 6&10 and 8&10 linked there, I also see 2 orange wires going to terminal 9?. If you have a Mmeter you can see very quickly if the orange wire(s) terminal has 230V when the zone valves are switched, also where is the boiler circ pump fed from?.
Hi John - I think there's a parallex effect in the photo and the orange wires are actually in 10, at least that's what I assumed throughout the thread!
So far I have become convinced the boiler is wired to permanent live and is on all the time!
Agreed it would be good to check volts on 10 (or is it 9?!)
 
Hi John - I think there's a parallex effect in the photo and the orange wires are actually in 10, at least that's what I assumed throughout the thread!
So far I have become convinced the boiler is wired to permanent live and is on all the time!
Agreed it would be good to check volts on 10 (or is it 9?!)
You are right Basher, the orange ones are on 10! And of course I could check whether there is voltage on 10 (I am just a bit reluctant to open an electric panel before switching off supply, I never usually do that...), although I am totally convinced that there is, following all the logic of a standard S-Plan. But the voltage on 10 is not taken anywhere, so I am now convinced that the solution would be to connect terminal 10 on my S-Plan wiring to the Switched Live terminal on my boiler (x2 connector no 1 on the Intergas Compact HRE). Question 1: Would you concur from what you can see?
I have also thought about how the UFH zone valve could be brought into play, as this valve is directly connected via L, N, E, only to the UFH wiring centre. If I connected the grey wire from this valve (currently unused) to terminal 1 permanent live (alongside the grey wires from the other two valves), and the orange wire (currently unused) to Terminal 10 (alongside the orange wires from the other two valves), I believe that the microswitch in the UFH zone valve would close when the valve is activated, and provide a live to the no 10 terminal, just as the other two valves do via their orange wires. Question 2: Does this make sense to you?
I have read the boiler instructions, and connecting one wire from the wiring centre to one connector in the boiler is a 5 minute job. No other wires would have to be changed. I may have to take out the link between 6 and 7 on the x4 connector, which I believe makes the boiler think that it needs to be permanently on. I would obviously do this with the power supply turned off. This should then result in the boiler coming on and off when valves are opening or closing. Question 3: Does this make sense, and would this require any other setting change to the boiler?
Thanks for all the help, it is all clear in my head now, would just appreciate some additional views!
 
Speaking as a non-expert (but as an engineer, kept warm by an Intergas HRE 40SB)
1) Yes
2) Yes (but only if the UFH wiring centre is on the same Consumer Unit breaker)
3) Yes, No

there is a regs/safety issue that the boiler system should be isolated by a single switch (eg fcu), and so 'injecting' live mains from another part of the house, that has separate isolation, would be a safety problem. Might be acceptable as a one-off experiment to prove it works, but not a permanent solution. That's why i suggested a wireless link to close the circuit in the boiler wiring centre, making isolation of the supply legit.
 
Last edited:
Speaking as a non-expert (but as an engineer, kept warm by an Intergas 40SB)
1) Yes
2) Yes (but only if the UFH is on the same Consumer Unit breaker)
3) Yes, No
Basher, thanks, and you touched on the one thing that I also just thought about. The earth, live and neutral to the UFH zone valve is provided from the UFH wiring centre, which does not have the same power supply feed as the S-Plan wiring. The are both in the garage, but have different isolation switches. I switch off one circuit breaker in the kitchen to remove power from all of the garage (and indeed other parts of the house). Is that what is meant by being on one Consumer Unit breaker?
 
Basher, thanks, and you touched on the one thing that I also just thought about. The earth, live and neutral to the UFH zone valve is provided from the UFH wiring centre, which does not have the same power supply feed as the S-Plan wiring. The are both in the garage, but have different isolation switches. I switch off one circuit breaker in the kitchen to remove power from all of the garage (and indeed other parts of the house). Is that what is meant by being on one Consumer Unit breaker?
I've added a little to my previous post since you probably first read it.
The major issue is regulatory, which i tried to cover in that additional note.

the other is practical, and basically about taking current from one house circuit (eg garage) and returning it through another (eg kitchen), which can cause residual current devices to trip. And it's not supposed to be done!

Could you just clarify, if you switch off Mains power to the garage in the main 'fusebox', does that turn off the boiler as well? Ie that would mean they are on separate circuits.
 
the other is practical, and basically about taking current from one house circuit (eg garage) and returning it through another (eg kitchen), which can cause residual current devices to trip. And it's not supposed to be done!

Could you just clarify, if you switch off Mains power to the garage in the main 'fusebox', does that turn off the boiler as well? Ie that would mean they are on separate circuits.

there is a regs/safety issue that the boiler system should be isolated by a single switch (eg fcu), and so 'injecting' live mains from another part of the house, that has separate isolation, would be a safety problem. Might be acceptable as a one-off experiment to prove it works, but not a permanent solution. That's why i suggested a wireless link to close the circuit in the boiler wiring centre, making isolation of the supply legit.
If I trigger the first consumer unit circuit breaker in the main fusebox (which just happens to be n the kitchen), all power to our extension, the garage and also the UFH, the boiler, and the CH/HW programmer. goes off.

The switch for the boiler would still shut everything down, as the live feed going into the valve microswitch (grey wire) would be taken from the wiring centre. Switch-off - no supply to the grey cable - no power to the boiler - or am I misunderstanding something. The only think that would still happen (but that is the same today!) is that the UFH valve can open, as it is supplied from the UFH wiring centre.

Which rings me to another idea: Why do I not wire the UFH valve into the S-Plan just as the other two, feeding from the same power supply as everything else, and use the cable to the UFH wiring centre as the boiler enable (i.e. thermostat) cable? That would sound straightforward and 'cleaner', except that the John Guest UFH wiring diagram (attached above) says not to wire the boiler enable connection into the wiring centre...I had no idea why not, it would work just like the hot water stat...Any idea?
 
If I trigger the first consumer unit circuit breaker in the main fusebox (which just happens to be n the kitchen), all power to our extension, the garage and also the UFH, the boiler, and the CH/HW programmer. goes off.

The switch for the boiler would still shut everything down, as the live feed going into the valve microswitch (grey wire) would be taken from the wiring centre. Switch-off - no supply to the grey cable - no power to the boiler - or am I misunderstanding something. The only think that would still happen (but that is the same today!) is that the UFH valve can open, as it is supplied from the UFH wiring centre.

Which rings me to another idea: Why do I not wire the UFH valve into the S-Plan just as the other two, feeding from the same power supply as everything else, and use the cable to the UFH wiring centre as the boiler enable (i.e. thermostat) cable? That would sound straightforward and 'cleaner', except that the John Guest UFH wiring diagram (attached above) says not to wire the boiler enable connection into the wiring centre...I had no idea why not, it would work just like the hot water stat...Any idea?
Thanks.
Clarity - it's all on the same breaker in the fusebox, good.
So a reasonable idea to take a (L) from the boiler wiring centre to the UFH valve microswitch, and from the valve orange Back to join terminal (10). Worth a try!

The safety issue remains in that someone working on the UFH wiring centre might turn off the local switch (fcu?) to work on it, and unexpectedly find live wires (from the boiler). I'll be told off for suggesting that might be mitigated by labelling.

I would personally favour this mains option, rather than delving into the JG UFH box, otherwise I suggest involving a heating professional for advice.
 
The safety issue remains in that someone working on the UFH wiring centre might turn off the local switch (fcu?) to work on it, and unexpectedly find live wires (from the boiler). I'll be told off for suggesting that might be mitigated by labelling.
Thanks Basher, why would there still be a live wire from the boiler? The only live wire not switched off by the boiler switch would be the feed to the UFH zone valve, but the microswitch (grey to orange) would no longer close as grey would not receive a live feed any more, and thus no orange would be live. Again, I may be missing something?
But to be fair, you have a very valid point, as there is a safety concern around the wire to the UFH valve, which could be live even when the boiler switch is triggered. This problem is already in place today, of course, and made worse by the fact that the connection between the UFH valve and the UFH wiring centre is made through the terminals 11 and 12 in the S-Plan wiring centre!!!

This may be a reason to actually pursue the thought of wiring the valve fully into the S-Plan, and only connect to the UFH wiring centre via the 'volt free' boiler enable link. So if no current exists in the S-Plan wiring centre, no current will ever flow back from the UFH wiring centre. I have contacted John Guest for advice on this, but I am more and more certain that this is the right way of doing it. It would be easily executed, as I could use the existing cable to the UFH valve for the boiler enable link, and connect the UFH valve locally to the S-Plan wiring which is right next to the valve!).
 
OP .... you seem to have made up your mind what you are going to do so crack on with the bang test

AND you shouldn’t have 2 points of supply to your central heating system - it tends to irritate the guys who service them as they don’t like getting shocks ....
 
Thanks Basher, why would there still be a live wire from the boiler? The only live wire not switched off by the boiler switch would be the feed to the UFH zone valve, but the microswitch (grey to orange) would no longer close as grey would not receive a live feed any more, and thus no orange would be live. Again, I may be missing something?
But to be fair, you have a very valid point, as there is a safety concern around the wire to the UFH valve, which could be live even when the boiler switch is triggered. This problem is already in place today, of course, and made worse by the fact that the connection between the UFH valve and the UFH wiring centre is made through the terminals 11 and 12 in the S-Plan wiring centre!!!

This may be a reason to actually pursue the thought of wiring the valve fully into the S-Plan, and only connect to the UFH wiring centre via the 'volt free' boiler enable link. So if no current exists in the S-Plan wiring centre, no current will ever flow back from the UFH wiring centre. I have contacted John Guest for advice on this, but I am more and more certain that this is the right way of doing it. It would be easily executed, as I could use the existing cable to the UFH valve for the boiler enable link, and connect the UFH valve locally to the S-Plan wiring which is right next to the valve!).
Hi Cheshire
I didn't get that there is already a direct connection between the UFH wiring centre and the boiler wiring centre!
The scenario I was concerned about was when boiler/kitchen circuitry left on, garage UFH locally isolated for maintenance. But no point in debating as they are already interconnected wiring centres!

Sorry I may be misunderstanding your suggestion. If you implement the 'volt free' signalling from UFH to boiler but still have orange wires terminal (10) to boiler switched live, the UFH can surely only come on when one of the others demands heat as well, and when the UFH goes off, it all goes off!
I hope I'm wrong!
 
From your initial description, the most likely scenario is that your boiler has been wired without any external control switching into X2 (volt free) or X3 (240v) Consequently the boiler is just operating 24/7 on the flow temperature thermostat. A rather inefficient mode of operation.

The motorised valves have presumably then been wired independently, to allow boiler output to flow into the heating system.

The easiest way to check this is to ask your installer to ckeck or confirm if the boiler X2 and X3 terminals are both bridged across the input pins.

Thereafter, it can be conventionally (S Plan?) rewired to respond to room thermostat inputs.

Alternatively to test this therory, turn all room thermostats to their lowest setting and the boiler thermostat to its highest setting. Even with no hot water demand and no heating demand, as the boiler flow temperature cools, the boiler will fire.
 
Last edited:
Hi Cheshire
I didn't get that there is already a direct connection between the UFH wiring centre and the boiler wiring centre!
The scenario I was concerned about was when boiler/kitchen circuitry left on, garage UFH locally isolated for maintenance. But no point in debating as they are already interconnected wiring centres!

Sorry I may be misunderstanding your suggestion. If you implement the 'volt free' signalling from UFH to boiler but still have orange wires terminal (10) to boiler switched live, the UFH can surely only come on when one of the others demands heat as well, and when the UFH goes off, it all goes off!
I hope I'm wrong!

The signal from the UFH would have to operate a relay with one set of contacts wired like the zone valve "end switch" ie a grey permanent live to one side and a yellow (switched) from the other side to terminal 10, that way all three zones are independent.??
 
Hi John.g
As I understand it, the grey and orange wires on the UFH 2-port valve are currently unused, so could be connected directly to L and terminal 10. Simples!
 
Grand so, that's the way to do it alright.

Does the boiler still need a permanent live though as well as the (proposed) switched live, most boilers do for overrun etc.
 
In cases like this I tend to go in, identify all the inputs and then disconnect everything before starting from scratch.
Then I know it's right.
 
Grand so, that's the way to do it alright.

Does the boiler still need a permanent live though as well as the (proposed) switched live, most boilers do for overrun etc.
Yes, that is the proposal.
[automerge]1603309957[/automerge]
You are right Basher, the orange ones are on 10! And of course I could check whether there is voltage on 10 (I am just a bit reluctant to open an electric panel before switching off supply, I never usually do that...), although I am totally convinced that there is, following all the logic of a standard S-Plan. But the voltage on 10 is not taken anywhere, so I am now convinced that the solution would be to connect terminal 10 on my S-Plan wiring to the Switched Live terminal on my boiler (x2 connector no 1 on the Intergas Compact HRE). Question 1: Would you concur from what you can see?
I have also thought about how the UFH zone valve could be brought into play, as this valve is directly connected via L, N, E, only to the UFH wiring centre. If I connected the grey wire from this valve (currently unused) to terminal 1 permanent live (alongside the grey wires from the other two valves), and the orange wire (currently unused) to Terminal 10 (alongside the orange wires from the other two valves), I believe that the microswitch in the UFH zone valve would close when the valve is activated, and provide a live to the no 10 terminal, just as the other two valves do via their orange wires. Question 2: Does this make sense to you?
I have read the boiler instructions, and connecting one wire from the wiring centre to one connector in the boiler is a 5 minute job. No other wires would have to be changed. I may have to take out the link between 6 and 7 on the x4 connector, which I believe makes the boiler think that it needs to be permanently on. I would obviously do this with the power supply turned off. This should then result in the boiler coming on and off when valves are opening or closing. Question 3: Does this make sense, and would this require any other setting change to the boiler?
Thanks for all the help, it is all clear in my head now, would just appreciate some additional views!
Hi Cheshire
The consensus seems to be that what you described earlier is the way to go.
ie get electrician to:
Replace present 3 core cable to boiler with 4 core to carry both a perm live, and a switched live from terminal 10
wire UFH valve grey wire to live
wire UFH valve orange wire also to term 10 (there may be a spare core to implement that?)
job done!
 
Last edited:
OP .. you seem to have made up your mind what you are going to do so crack on with the bang test

AND you shouldn’t have 2 points of supply to your central heating system - it tends to irritate the guys who service them as they don’t like getting shocks ..
I think I will rather continue to seek advice than do a bang test - very grateful for the hints and tips, which is exactly what helped me discover the two point of supply issue. It was not me who wired it up in the first place!
[automerge]1603317033[/automerge]
Yes, that is the proposal.
[automerge]1603309957[/automerge]

Hi Cheshire
The consensus seems to be that what you described earlier is the way to go.
ie get electrician to:
Replace present 3 core cable to boiler with 4 core to carry both a perm live, and a switched live from terminal 10
wire UFH valve grey wire to live
wire UFH valve orange wire also to term 10 (there may be a spare core to implement that?)
job done!
Indeed, all of that, plus I believe replace power supply to UFH valve with power supply from wiring centre (solving the two supply source issue, I do think this needs to be done for safety), and use cable between UFH wring centre and S-Plan wiring centre to connect to boiler enable on the UFH wiring centre, wiring it into S-Plan like a thermostat for another zone.
[automerge]1603317802[/automerge]
Regarding power supply: I noticed that switching the boiler feed off near the boiler does not switch off the power to the central heating and hot water programmer (which is in the kitchen). Clearly the programmer is connected as without a live signal from it nothing central heating and hot water would not work. If the programmer is still on when the boiler feed is disconnected, does this not mean that the wiring centre may still get a live feed?
I might be wrong here, but if not, I am starting to wonder how this was all signed off - which it was, I remember the electrician going round for almost a day with another electrician who certified it all.
[automerge]1603360824[/automerge]
I had a look into all the wiring today, including inside the boiler. All as expected and supporting the solution above. However, this also confirmed that the power supply to the programmer is indeed made locally in the kitchen (same consumer circuit breaker, but not isolated by boiler switch). So a live feed could be sent even when boiler switch is off. Luckily I isolated the consumer unit circuit breaker at all times when investigating the system.
The cable running from programmer to S-Plan wiring centre is only three core plus earth. So if I wanted to supply power to the programmer from the S-Plan wiring centre as it should be done, I could not run a neutral wire. In this context, would it be acceptable to use the neutral from the local supply?
 
Last edited:
the dreaded 'borrowed neutral'
before answering, I wondered what model the programmer Is, and how it is wired. If it just switches the wiring centre via 'volt free' contacts with the live coming from the wiring centre and returning via the appropriate core, there would not be a hazard in the way you describe.
 
the dreaded 'borrowed neutral'
before answering, I wondered what model the programmer Is, and how it is wired. If it just switches the wiring centre via 'volt free' contacts with the live coming from the wiring centre and returning via the appropriate core, there would not be a hazard in the way you describe.
It’s a bog standard one, mine is iflo but the Drayton ones look identical. Definitely not volts free...it is the live feed going through for CH and HW. I am puzzled how this could be wired up like this only two years ago. As I said, luckily I removed circuit breaker before looking at wiring and did not touch anything before building up a through understanding, but the wiring centre could definitely be receiving a live feed from programmer even when boiler switch is off!
 
That is a pain. I agree you need another wire!
The system should have been done to the wiring regs, so I don't understand why you've ended up like this, unless due to 'organic growth' of the heating.

The 'borrowed neutral' is not the proper way as I'm sure you appreciate. In this instance it would work because both loads are on the same breaker, but not recommended - those more knowledgeable might like to comment?

Would it be practical to move the programmer to be nearer the wiring centre?

Alternatively if you were considering updating the system, eg to control individual radiators, then wireless could solve the issue.
 
Thanks Basher, I am not going to pursue the borrowed neutral idea. I am not quite knowledgeable enough to really understand why this would be problematic, but it would certainly be confusing.
I will indeed go wireless for the heating control, which would leave me with a spare wire to the boiler wiring centre to connect the neutral correctly for the hot water control. Most probably, I will even move the entire programmer to the garage next to the boiler, we do not really need to access hot water controls all the time, this runs on a timer and rarely gets changed. And my wife would rather like an extra socket in the place of the apparently very ugly programmer, and the fact that the programmer is locally supplied, with power not linked to the boiler, will allow this to be done!
[automerge]1603380401[/automerge]
Deciding whether to move and keep the programmer next to the boiler and keep a manual on/off option available or go wireless and just connect the wireless receiver. I will be using a Lightwave RF boiler switch (as I have loads of Lightwave TRVs already) for CH, but not sure what to use for HW. Thinking of a wireless relay but worried about no manual override option. Any ideas?
 
Last edited:
Deciding whether to move and keep the programmer next to the boiler and keep a manual on/off option available or go wireless and just connect the wireless receiver. I will be using a Lightwave RF boiler switch (as I have loads of Lightwave TRVs already) for CH, but not sure what to use for HW. Thinking of a wireless relay but worried about no manual override option. Any ideas?
[/QUOTE]
No immediate bright ideas. It's a shame Lightwave don't do a combined heating and HW link. There are other brands doing this, but I guess would't integrate with what you're suggesting.
I used a Lightwave electric switch LW934 to control a water heater, and scheduled it with the app, but that won't integrate with a Lightwave thermostat controlling the boiler switch. And the boost button would be your phone!

If you decide to put a 13A socket where the programmer is (make sure the cable is 2.5mm) don't you then have a spare 3 core to the boiler wiring centre? In which case you could buy an electronic boost button and hard wire it! This sort of thing: Sangamo Powersaver Electronic Boost Timer 30min to 2 Hour - https://www.tlc-direct.co.uk/Products/SGPSB.html . I understand if this doesn't appeal!
 
I used a Lightwave electric switch LW934 to control a water heater, and scheduled it with the app, but that won't integrate with a Lightwave thermostat controlling the boiler switch. And the boost button would be your phone!
Oops, why does it not integrate with boiler switch/thermostat? I just put a saved search on eBay for the LW934 as it is no longer sold anywhere. Is it not just like a timed switch that you can schedule, activate via app, or indeed press manually?
 
Oops, why does it not integrate with boiler switch/thermostat? I just put a saved search on eBay for the LW934 as it is no longer sold anywhere. Is it not just like a timed switch that you can schedule, activate via app, or indeed press manually?
it does all those things - schedule, activate by app, and press manually, yes. Sorry, the integrate comment is misleading - I was thinking you might want to 'talk to it' via the boiler switch/thermostat.
The one thing about it, is that it has a temperature sensor, and turns off once the set temp is reached. It goes up to 40 or 45 deg C. So if you set it to max, the room never gets to that temp. so it continues switched on until the schedule activates 'off'.
I've got an unused LW934 if you want one! It was one of the few first series Lightwave devices which were Homekit compatible. I hope they don't stop supporting it.
 
Know nothing but taking a flier, the U.K. orange wires go to 10 . Why don’t you take the wires out of 10 and see if the boiler fires taking due care with 240 volts . I always with loose wires pop them into Wago connectors.
but read below first
If the boiler fires when the valve is closed then there is a feed from the valve directly to the boiler (possibly from another position.

if the boiler doesn’t fire, then something I’d connecting 10 to the boiler.


my system (y type) connects using 4 core to provide both LNE and switched live ( using a yellow core which nearly looks orange)

could it be that one orange is actually the switched live to the boiler?

this could explain that you need to put on one valve manually.

you say you have 3 valves - where is the 3 orange?

Probably a load of rubbish but you never know!
 
Last edited:
Good evening, I implemented everything that was discussed in this thread, but my last step, connecting a switched live to the boiler from where the orange cables terminate, is failing. I installed a new cable with four cores to the boiler today, and I connected the switched live from the oranges in the S-Plan wiring centre to terminal 1 on the x2 connector. I also removed the link between 6 and 7 on the x4 connector as per the Intergas manual. The boiler fired up just fine, ran for a while, but after about half an hour suddenly all power to the boiler and to the new hot water switch (fed by same mains power) was cut out. I removed and reinstalled the same fuse, and funnily enough (I cannot explain this at all), the power was back, and the same thing happened again, half an hour of running and then the power cut out again. Just the power feed to the boiler on the fused spur. I then suspected the spur switch and replaced it with another one. No joy, by now things would not start up again at all. I then removed the power to the boiler from the wiring centre - power was back when I put the circuit live again. I reconnected the boiler, and power cut out again immediately...Interestingly, the fuse is not blown. I tried various fuses in the process, so it was not down to one specific one. How can the power to the entire wiring centre be cut, with the fuse remaining operational?

I now returned everything to the original state, no switched live and reconnected 6 and 7 on the X4...

Can anybody make any sense of this?

Thanks, Henrik
 
I reconnected the boiler, and power cut out again immediately...Interestingly, the fuse is not blown. I tried various fuses in the process, so it was not down to one specific one. How can the power to the entire wiring centre be cut, with the fuse remaining operational?

What is tripping? MCB? RCD?
 
What is tripping? MCB? RCD?
Nothing is actually tripping. The fuse in the spur is also intact. Just a ll the devices connected to the spur stop working. Last night, I fully disconnected the boiler, other devices were fine again. Then I put everything in the boiler back to the state it was in before (6,7 connector on x4 back in, removed switched live from 1 in x2), and connecter it all into the wiring centre in the same places as yesterday. Now the boiler is running again, in the old (non-switched) manner. I just cannot explain at all why other devices lose mains power, too, without anything actually tripping...
 
Nothing is actually tripping. The fuse in the spur is also intact. Just a ll the devices connected to the spur stop working. Last night, I fully disconnected the boiler, other devices were fine again. Then I put everything in the boiler back to the state it was in before (6,7 connector on x4 back in, removed switched live from 1 in x2), and connecter it all into the wiring centre in the same places as yesterday. Now the boiler is running again, in the old (non-switched) manner. I just cannot explain at all why other devices lose mains power, too, without anything actually tripping...
Could it be a dodgey connection? Maybe a bit of sleeving slightly under a screw terminal somewhere? Otherwise needs diagnosis with a tester or multimeter when it's in 'fault' mode!
 
This is a possibility of course, but I am trying to understand the logic...Why would there be no more feed to the hot water switch if the boiler connection was 'dodgy'? Why did the 3 AMP fuse not blow (get destroyed)? Could a short circuit of some kind create a scenario in which this could happen?
 
This is a possibility of course, but I am trying to understand the logic...Why would there be no more feed to the hot water switch if the boiler connection was 'dodgy'? Why did the 3 AMP fuse not blow (get destroyed)? Could a short circuit of some kind create a scenario in which this could happen?
Sorry I wasn't suggesting there was anything wrong with the boiler connections. I was thinking more of the mains supply to the spur, and wonder if anything had been disturbed during removal of the original programmer, unless I have misunderstood the extent of your upgrade.
 
Nothing is actually tripping. The fuse in the spur is also intact. Just a ll the devices connected to the spur stop working. Last night, I fully disconnected the boiler, other devices were fine again. Then I put everything in the boiler back to the state it was in before (6,7 connector on x4 back in, removed switched live from 1 in x2), and connecter it all into the wiring centre in the same places as yesterday. Now the boiler is running again, in the old (non-switched) manner. I just cannot explain at all why other devices lose mains power, too, without anything actually tripping...

What do you mean by the non-switched manner?, is the boiler now stopping/starting from the programmer/mid position valve in all modes or have you a permanent live from somewhere and the boiler is permanently on just starting/stopping on its boiler stat?.
 

Reply to No switched live to boiler? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
149
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
99
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
195
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
251
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...