You probably have the continuous ventilation unit on summer boost mode.

The continuous ventilation unit that you have has a large set of filters in it. These filters need to be cleaned regularly. If they become blocked or partially blocked, the pressure differential across the filters rises and the unit cuts out. If the unit fails to cut out, the exchanger will start to freeze over, to such an extent that the defrost cycle does not clear the exchanger of frost.

Consequently hot lines start to become cold and cold lines hot - in simple terms lines that don’t normally require insulation chill and condense in the atmosphere.

From your photos the hot line insulation into the Panasonic booster is well undersized. this should be at least 60mm diameter isoprene insulation Additionally the Panasonic unit should have at least 100mm of clear well ventilated space around it to function properly. Whatever is blocking the right hand side should be removed.

Not being picky, but the electrical isolation switch should be above or to the side of the unit It should not be underneath the drain point.

The quick solution is to turn off the two units and let them both return to room temperature (that may take 24 hours). The filters then need to be removed and properly cleaned or replaced.

If the unit is still operating with blocked or partially blocked filters it is likely that the pressure sensors are defective or have been removed ( people remove them to get the fan going not realising that the filter is the issue) They need to be reinstated.

I assume that you have recently moved into the property - these units are very good, but they need regular maintenance. Ask your neighbours, there will be a heating / ventilation man who regularly visits the building to undertake that routine work two or three times a year.

If you need any further clarification get back to me or indeed call Triton, they are expensive, but will come and clean / reconfigure the system for you

A final point - don’t go round insulating every pipe you can see - the condensation is almost certainty because the system is not functioning properly. You need to address the cause first, then the symptoms.
 
Last edited:
Hi,


You probably have the continuous ventilation unit on summer boost mode.

The continuous ventilation unit that you have has a large set of filters in it. These filters need to be cleaned regularly. If they become blocked or partially blocked, the pressure differential across the filters rises and the unit cuts out. If the unit fails to cut out, the exchanger will start to freeze over, to such an extent that the defrost cycle does not clear the exchanger of frost.

Consequently hot lines start to become cold and cold lines hot - in simple terms lines that don’t normally require insulation chill and condense in the atmosphere.

From your photos the hot line insulation into the Panasonic booster is well undersized. this should be at least 60mm diameter isoprene insulation Additionally the Panasonic unit should have at least 100mm of clear well ventilated space around it to function properly. Whatever is blocking the right hand side should be removed.

Not being picky, but the electrical isolation switch should be above or to the side of the unit It should not be underneath the drain point.

The quick solution is to turn off the two units and let them both return to room temperature (that may take 24 hours). The filters then need to be removed and properly cleaned or replaced.

If the unit is still operating with blocked or partially blocked filters it is likely that the pressure sensors are defective or have been removed ( people remove them to get the fan going not realising that the filter is the issue) They need to be reinstated.

I assume that you have recently moved into the property - these units are very good, but they need regular maintenance. Ask your neighbours, there will be a heating / ventilation man who regularly visits the building to undertake that routine work two or three times a year.

If you need any further clarification get back to me or indeed call Triton, they are expensive, but will come and clean / reconfigure the system for you
Thank you so much! This is super helpful. Yes, we just moved in. It's a new build and the developer has been so useless and unhelpful. It sounds like I need an engineer from Triton to come out as I would not even know where to start with the filters. I'll give them a call.
 
Where about’s are you? If you are in London and you want someone to look at the installation and talk you through how to operate / maintain it get back to me. We have a Mr Expert on Titon systems - he is old, but he knows them inside out!
 
Last edited:
Where about’s are you? If you are in London and you want someone to look at the installation and talk you through how to operate / maintain it get back to me. We have a Mr Expert on Triton systems - he is old, but he knows them inside out!
Yes, I am in NW2 - that would be great - please let me have his details. Tried to contact you privately but it would not work.
 
It looks like you have a chiller system for cooling.

Best thing for this is Cork Tape.
Wrap it around the pipes and valve bodies loosely and then squeeze it firm.
You may have to do the condensate drain also from the fan coil for the first 1/2 metre or so.

The water from the chiller will be @ 12 C, so it will condensate when ever you use the cooling system.
 

Reply to Please help me diagnose these drips and condensating pipes! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hiya - posting in this forum as I'm guessing this relates to my neighbour above's boiler, but I may be wrong so please say if so. Basically the...
Replies
1
Views
178
Hi, I have a PRV located in a heated plant room that is between a pair of stop cocks. It was installed to keep pressure under 3 Bar a couple of...
Replies
9
Views
506
S
We had water leak from the laundry sink into the cupboard below, then flow down the hole cut for the pipes (the hole was on the floor of the...
Replies
1
Views
441
James Auberon
J
i can't tell if my shower tap (cock stop) is leaking or not ...............so after showering, the shower head will drip fast for 2 hours, then...
Replies
0
Views
272
Hello all, first time poster so if there is any additional information I can provide that may help, please let me know. Our kitchen mixer tap has...
Replies
3
Views
483
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock