Hi yes I now believe I have a open vent system. The pump is fed from a 3rd cable not visible in the photos direct from the boiler the 2 cables from the boiler are:
It's a 3 core cable with only brown used and connected to HW on from the Hive number 5 in the terminal block
The other cable is connected :
8 earth
9 permanent neutral
10 permanent live
Now I've looked the wiring seems very odd the cylinder thermostat is connected to the terminal block but then nothing.
So top to bottom
1 brown/live from cylinder stat
2 earth from cylinder stat
3 CH on from hive on the left, brown to the motorised valve on the right.
4 empty
5 HM on from hive, brown single cable to boiler
6 nothing left, blue with red tag from cylinder stat on right.
7 empty
8 earth
9 permanent neural from hive on left to the boiler on right
10 permanent live from hive on left to the boiler on right.
So this is what I think is happening. The system has been set up to run HW or HW and CH. So the controller provided a signal via terminal block 5 to the boiler to fire up, this happens for both HW
and CH. The CH element is controlled by a live feed from the controller to open the motorised valve.
This all seems wrong but has been working. So I now think I have 2 problems. First the random firing of the boiler and second the wiring of the system.
I'm thinking I should have a second motorised valve controlling HW.
Oh and only 3 of the 5 wires from be motorised valve are used.
It's a 3 core cable with only brown used and connected to HW on from the Hive number 5 in the terminal block
The other cable is connected :
8 earth
9 permanent neutral
10 permanent live
Now I've looked the wiring seems very odd the cylinder thermostat is connected to the terminal block but then nothing.
So top to bottom
1 brown/live from cylinder stat
2 earth from cylinder stat
3 CH on from hive on the left, brown to the motorised valve on the right.
4 empty
5 HM on from hive, brown single cable to boiler
6 nothing left, blue with red tag from cylinder stat on right.
7 empty
8 earth
9 permanent neural from hive on left to the boiler on right
10 permanent live from hive on left to the boiler on right.
So this is what I think is happening. The system has been set up to run HW or HW and CH. So the controller provided a signal via terminal block 5 to the boiler to fire up, this happens for both HW
and CH. The CH element is controlled by a live feed from the controller to open the motorised valve.
This all seems wrong but has been working. So I now think I have 2 problems. First the random firing of the boiler and second the wiring of the system.
I'm thinking I should have a second motorised valve controlling HW.
Oh and only 3 of the 5 wires from be motorised valve are used.