I'm doing my ACS and have an issue with pressure loss calculations!!
sample question : "what would the pressure loss per meter be on copper tube of 15mm feeding a 12kw (gross) gas hotplate"
I can't for the life of me get the correct answer.....
I nett the hotplate 10.81kw divide that by 9.7 to get 1.11M3/h I then use the pipe length table which shows 15mm 1.3M3/h is maximum length of 12meters.
That means (i think) in 12meters of 15mm copper the loss is 1mb, so if i divide 1 by 12 it gives me 0.0833mb drop per meter ??
but the answer is 0.1042mb
I look forward to your help.....
12 kw gross
10.90 kw net
15mm at 10 m with 1 mbar drop 1.1 m3/h
1.1 divided by 10 = 0.11 mbar drop
you need to divide 1.3 by 12 not 1 = 0.1083 m bar
where does the 1.3 come from?
1.3 m3/h at a max length of 12m
So you have 12 m of copper and at the end of it you can pass / pull off 1.3m3/h with your 1 mbar pressure loss
Eg the capacity of the pipe at 12m
I thought the maximum lengths on the table were equivalent to 1mb drop?
this will confuse you now :D
To estimate pressure loss across a pipe leg
(mbar) = (328785 ÷ dia + 7558) x m3/h x m3/h ÷ dia ÷ dia ÷ dia ÷ dia ÷ dia x Length
so
328785 divided by the dia of the pipe (15mm) plus 7558 = 29477
29477 x 1.3 x 1.3 = 49816.13
49816.13 divided by the dia of the tube 5 times then times by the length
49816.13 ÷ dia ÷ dia ÷ dia ÷ dia ÷ dia x 1 = 0.065 mbar per m of 15mm
  • PipeSizingComm.pdf
this one might be better
  • Domestic Gas Planning And Sizing.pdf
if i do the question on my Anton app it comes out at 0.1042
exactly as the question states!! I'm glad its not just me but won't help me for the exam :(
It’s all aprox especially when your working by the m
Reply to Pressure loss on gas pipe (BS 6891 pipe sizing) in the Plumbing Jobs | The Job-board area at PlumbersForums.net