Discuss Radiator banging / clicking - possible reaction to F1 protector? in the USA area at PlumbersForums.net

Messages
32
Hi.

We’ve had rather a lot of noise issues with our radiators since we had a new boiler installed. Our radiators other than 2 more recent ones are all over 30 years old.

When the boiler got installed in the middle of 2020, after the first few days, we had several loud airlocks each day. Probably up to 10 times in total until we got the plumbers round to sort it out. I can’t remember exactly what they did, but the air locks stopped occurring then. But what then was the case was that whenever the heating was on, the main radiator that must remain on all the time seemed to have a sound similar to a cold tap permanently running. That sound was amplified to the room above, unless the TRV on this radiator was either on 5 or totally off.

We got the plumbers back, and they then drained the system (not a blast out though) and added some Fernox F1 Protector.

This seemed to remove the issue I described with the sound like a tap was running, but introduced a whole load more.

The system clicks and bangs occur very regularly when the heating is on. It however is much more noticeable in my bedroom, but the noise is very similar in many other places in the house. It is not coming from the radiators, but they are what makes it more audible as upstairs all the pipes are under the floorboards. The F1 Protector I’m guessing caused some sort of chemical reaction. Every single day, loads of air / gas was generated and the radiators could be bled very frequently with more build up of whatever this was. The water was also very dark grey and smelt strong. We kept dealing with this throughout the winter ourselves and although the noise remained, the issue with the gas does seem to have gone now, probably because the radiators hadn’t been used this last summer.


Now, the clicking decreases when the heating is off at the boiler, but it still clicks or bangs randomly usually at least once an hour through the night. Sometimes it can be incredibly loud.



From what I’ve read, this now could be many things:


Boiler kettling – It seemed that F1 protector it supposed to help with this, but it seemed putting that in caused trapped air and other nasty reactions.

Expanding / shrinking pipes – This sounds like it could indeed be the case. As I can lift and move my radiator slightly and feel it rubbing in the hole in the floorboards, and I can almost create the identical sounds myself by doing this. However, the radiators and pipes have not changed since our boiler got replaced, so as that is the case, I can’t understand why this should be related. Our heating with our old boiler just bade a very quiet and consistent tinkling while on, and no noise when off.

Dirty pipes – While we had the F1 protector put in supposedly to clean the system, given the reaction it caused, it probably has made it worse. We don’t have air / gas in the system now and the water seems clean, but I obviously can’t tell what the pipes are like. I don’t believe it is related to the radiators now, as I can turn them off at both the TRV and other valve and the noise still occurs from the pipes.


As it is a new boiler with very old pipes and radiators, it is hard to know if a full system flush will solve this issue. I know that these radiators and pipes can be quiet, and nothing physically should have changed about them. Just likely to be something in them.



This clicking / banging has been irritating me so much that I’ve done rather a lot of recordings of it. So I can explain what it is better.



This first link below is actually from last year. This was during the day when I was at my desk. The microphone easily picks up me pressing a few buttons on my keyboard, but then it just sounds like a hard metal object hits the radiator hard. The radiator is nowhere close to my microphone, which just shows how loud it can be. This is a good example of what can occur in the night.



This next clip is close up to the pipe when there was an obvious reaction of some sort. You can hear what sound like fragments rolling around in the pipes, spitting, gurgling and then this clicking and banging begins. The gurgling has long since stopped, but the banging and clicking remains.



Number 6 was only from a few days ago when the boiler was on, but my radiator off. I’ve edited the recording and joined many of the sounds closer together. They sound similar, but can vary a lot regarding how far apart they are.






This is an awful lot of information, but I’m really stuck with what this is most likely to be, and what sort of people would know most about it and be able to sort it.







Many thanks.
 
F1 is not designed to free off dirt or clean the system. If the water quality is poor then the system should have had a full powerflush when the boiler was changed IMO. Most likely the disturbance of the works has shifted crud that was hitherto deposited and not in circulation. I cannot see how F1 would caused the problem, however.
 
Thanks for the info.

Before our old boiler failed, we were not having these issues. So it has been quite difficult to work out what it is related to. The water system was totally drained when we got the new one installed, and that was when we for the first few days got a lot of airlocks occurring. After all this and a few other issues (the banging and clicking hadn't started yet) , they drained the system again and added the F1 protector and filled it back up. It only seemed to be a few days after this that all this banging, gurgling and clicking started to occur so frequently with rather dirty water. This was when there also seemed to be gas or whatever it was being generated daily as there were no leaks anywhere. After 2 summers of no heating being on, the radiators now full of just water again when on, but most of the noise is still there, but it seems to be in the pipes.

If it is related to dirty water or the reaction after the system was last drained with F1 added, then as the water was dirty at the time, it is entirely possible that the pipes will have a lot of that still in them. It hasn't been treated since this was added, but each attempt of anything at the time seems to have made it worse, so that is partly why it has been put off.

We considered new radiators, but then thought that if it was related to the pipes which are likely older than are 30+ year old radiators, it may make no difference at all.

The power flush seems to look like the best option, but we had one plumber round who would have been able to do that able to do that (though he was too busy then), but he admitted that he didn't have any idea what the issue could be, which surprised me a little. As the sound effects fit the description of several things I mentioned.



Any more advice would be much appreciated.



Many thanks.
 
I've only skim-read your essay (sorry, but a bit pressed for time today) but my suspicion is that your installers have left the pump on its highest setting rather than the lowest – preferably constant pressure or proportional pressure – one that achieves proper circulation. This will cause the whooshing noises in your pipework. The creaking and banging is probably due to the new boiler having a much lower heat capacity heat exchanger than your older one, which means the flow temperature will rise and fall more rapidly. Also, if the system is probably cycling on and off more than your previous boiler did. The creaking and banging (arising from so-called slip-stick friction) will occur when the pipework is heating or cooling.

You can probably mitigate the problems by carefully balancing the system (so the TRVs are normally open) and matching the pump setting to the emitter system properly. A full cure may need you to have a look at points where the pipework and radiators are attached to the fabric of the house and insert some hemp or felt to allow smooth sliding.

Use the search box on the top right of this page. These issues have been asked and answered many times on this forum.
 
I've only skim-read your essay (sorry, but a bit pressed for time today) but my suspicion is that your installers have left the pump on its highest setting rather than the lowest – preferably constant pressure or proportional pressure – one that achieves proper circulation. This will cause the whooshing noises in your pipework. The creaking and banging is probably due to the new boiler having a much lower heat capacity heat exchanger than your older one, which means the flow temperature will rise and fall more rapidly. Also, if the system is probably cycling on and off more than your previous boiler did. The creaking and banging (arising from so-called slip-stick friction) will occur when the pipework is heating or cooling.

You can probably mitigate the problems by carefully balancing the system (so the TRVs are normally open) and matching the pump setting to the emitter system properly. A full cure may need you to have a look at points where the pipework and radiators are attached to the fabric of the house and insert some hemp or felt to allow smooth sliding.

Use the search box on the top right of this page. These issues have been asked and answered many times on this forum.
Sorry for the long post! I'm not good at explaining things in brief, maybe because I think it isn't enough for me to understand though! But this has been happening for such a long time that i thought I would go into more depth.

They did replace the old pump with a new one. Our old one was on speed 2 and this one was put on Speed 3. We didn't know this until we checked it and changed it back to 2. But this was after the first lot of problems. We have had it on 2 for well over a year with this issue still happening.

The most confusing thing is that I've tried avoiding using my radiator in my room for nearly a week now, but that seems to make no difference to the noise at all. The only time the system goes totally quiet (and remains consistently quiet with no bangs or ticks at any point) is when the boiler hasn't been heating up the radiators and pipes for several days, which will be why summer was fine.

I could tolerate some quiet noise while our heating came on and turned off, which is pretty normal, but the fact that it continues to bang and clunk a few times an hour over night is why I myself am really struggling to tolerate it.

Now I have looked and tried to listen in more areas of the house, this very similar noise seems to be happening in many other pipes too. As the pipes never used to make these noises, and the fact that they haven't moved, it suggests to me that using foam / checking the hole size in the floorboards and other movement related things are less likely to be related.

Our heating used to come on and off a bit more regularly actually. We used to have a brief 30 minutes in the middle of the day as well as the longer in the mornings and evenings. Now we just have morning and evening. It does the same in the day between the times it is on as it does in the night. Less clicks, but often there will be one or two very loud bangs. It is odd as it shouldn't be related to the temperature changing if the radiators have been off for so long.

Just need to think very carefully before spending money on anything that we are not sure will fix the issue.
 
Our heating used to come on and off a bit more regularly actually. We used to have a brief 30 minutes in the middle of the day as well as the longer in the mornings and evenings. Now we just have morning and evening. It does the same in the day between the times it is on as it does in the night. Less clicks, but often there will be one or two very loud bangs. It is odd as it shouldn't be related to the temperature changing if the radiators have been off for so long.
The cycling I was referring to occurs every few hundred seconds within the longer periods the programmer is on.

I'm assuming the 'loud bangs' are coming from the pipework. If they are coming from inside the boiler, i.e. explosive ignition, it needs to be shutdown and investigated by a registered gas engineer as a matter of urgency.
 
The cycling I was referring to occurs every few hundred seconds within the longer periods the programmer is on.

I'm assuming the 'loud bangs' are coming from the pipework. If they are coming from inside the boiler, i.e. explosive ignition, it needs to be shutdown and investigated by a registered gas engineer as a matter of urgency.
The occasional loud bangs and more frequent quieter clicks all sound like they are only in the pipes. You can hear them through the radiators, but when listening closely, it is clear that the louder points is in the pipe work. So I don't think this is a serious problem, other than in my case being extremely annoying as the loud bangs can sometimes wake me up at night. I keep changing my mind on weather it is the pipes moving, as that according to what I read does make sense, but then as they never used to do this and the pipes haven't been touched, this shouldn't have changed. The loudest bangs do sound like metal buckling as if it is shrinking or expanding, but I'm unsure why it would do this in the middle of the night with over 4 hours between the heating going off and coming back on. If it isn't the pipes shifting, then can dirty water and a very small amount of air maybe stuck in them cause this?
 
If it isn't the pipes shifting, then can dirty water and a very small amount of air maybe stuck in them cause this?
No. Air tends to cause a 'trickling' sound. Occasionally a 'glugging' noise as a large bubble makes its way around the system.

Changing the boiler will have changed the operating temperatures of the pipes, the rate of change of those temperatures with time and the installer may have moved the ones near the boiler and/or anchored them more firmly at various points than they were previously cause the far ends to have to move more than previously to accommodate expansion / contraction.

Google 'central heating slip stick noise' or use the search box at the top right of the page. This is a common problem and the fix is a bit tedious but not difficult.
 
The occasional loud bangs and more frequent quieter clicks all sound like they are only in the pipes. You can hear them through the radiators, but when listening closely, it is clear that the louder points is in the pipe work. So I don't think this is a serious problem, other than in my case being extremely annoying as the loud bangs can sometimes wake me up at night. I keep changing my mind on weather it is the pipes moving, as that according to what I read does make sense, but then as they never used to do this and the pipes haven't been touched, this shouldn't have changed. The loudest bangs do sound like metal buckling as if it is shrinking or expanding, but I'm unsure why it would do this in the middle of the night with over 4 hours between the heating going off and coming back on. If it isn't the pipes shifting, then can dirty water and a very small amount of air maybe stuck in them cause this?

What make/output were/are the old/new boilers.

make/model of old/new circ pumps

Check that pump is pumping in the correct direction. (Towards either a mid position valve or towards two port valves)
 
Might seem a bit simplistic but also check that the boiler pipework is installed correctly, ie that the flow pipe is hotter than the return pipe.

Is it a open vented system or sealed with a expansion vessel?.
 
New posts

Reply to Radiator banging / clicking - possible reaction to F1 protector? in the USA area at PlumbersForums.net

Similar plumbing topics

Hi guys....we have an old Astracast sink top....I think its a composite sink....has a big single bowl. My wife thinks it looks scruffy....looks...
Replies
2
Views
225
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
459
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
257
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
170
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock