Is secondary return hot water a form of legionella control?
 
Correct will be around 47-55
 
It can be used to eliminate dead-legs and return doesn't need to be 60 to comply.
Generally a return is more likely to cause a risk than eliminate it but as always its not a one size fits all situation
 
(Disclaimer: From over a decade old memory)
55 will do and lagging is usually required, I don't think it has to be continuous either and so can be scheduled.
 
(Disclaimer: From over a decade old memory)
55 will do and lagging is usually required, I don't think it has to be continuous either and so can be scheduled.
Scheduled is ok. On horizontal unvented cylinders, even without a hot return, a pump is stipulated to circulate the tank and prevent stratification. It’s recommended to run the pump for an hour a day.
 
Legionella start to die off at 55°, but (from a decade old memory) it takes an hour.
I'm sure there's a rule about the stored water being at 60°C (why?). Is the 55°C you quote a rule for the secondary return?
 
Wouldnt it have to be the same time as the boiler is heating the cylinder?
othetwise you are just shifting water around and not heating it all up to 60
 
Wouldnt it have to be the same time as the boiler is heating the cylinder?
othetwise you are just shifting water around and not heating it all up to 60
Well if it's circulating at 55°C for an hour, that is enough to kill all the legionella. Probably if the cylinder is held at 60°C, then 55° is to allow for potential heat losses over the length of the pipe.

But yes, the timed circulation does logically have to take place at a time when the top of the cylinder is hot rather than when the cylinder has cooled (at night, say). In practice, it makes sense to run the secondary at the time when people are using hot water which should be during or soon after the cylinder heating.
 

Reply to Secondary return hot water in the USA area at PlumbersForums.net

Similar plumbing topics

Silly question (and might already been asked 100rds of time) - I am specifying a circulation pump for the hot water secondary (circulation) return...
Replies
12
Views
1K
R
Wb 4000 recently installed, and just balanced the rads with around 16 degree delta across most rads. I'm trying to make sure that the return...
Replies
0
Views
389
Return temperature
R
We have had an ongoing issue with low hot water temperatures in a school. During the recent repair of a leak, the plumbers isolated the hot...
Replies
2
Views
425
We have hot water, tank for hot water why is the hot water boiling hot from tap,and shower, We are on a schedule for hot water via our hive app...
Replies
4
Views
329
J
Need advice on secondary return issue. When secondary return pump is running no hot water flows from hot taps.when pump off the taps work. Anyone...
Replies
0
Views
726
JohnyC
J
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock