Hi
Just wondering can anyone tell me why a secondary return can not be plumbed with plastic pipe like pex or pb
 
Interesting exedon; so it sounds like it should be ok in a domestic situation with a timed or PIR operated pump- but not in a constant or commercial setting.
 
Yet the same type of pipe can be used in heating installations at presumably slightly higher temperatures and slightly lower pressures.

I've looked into this situation fairly deeply, a couple of years ago, and can find no manufacturers ( the ones I was going to use - not all ) that say their pipe can't be used in this situation.

If their pipe can't be used for secondary return systems, you would think they would emblazon the the fact that their product is not suitable.

Contact the Manufacturers of the product you want to use and get confirmation either way.
If they respond ( some didn't in my situation ), use the one's who say their product is suitable.
 
I've looked into this situation fairly deeply, a couple of years ago, and can find no manufacturers ( the ones I was going to use - not all ) that say their pipe can't be used in this situation.
Hep2O is one that says 'no':


"No. Continuously operated re-circulating systems (Secondary Hot Water Circulation/Ring main installations) are very different from conventional hot water supply and central heating systems found in domestic properties, for which Hep2O products have been tested."
 
Polypipe say no, see note 1 bottom of table

Polypipe.PNG
.......................................^^^^^^^^
 
Yes, but hep says “continually operated re-circulating circuits”

I would suggest this is not what one has in a domestic secondary return situation.
 
Mlcp or copper only plastic is a no unless it’s on a pir sensor and max run time of 5 mins which isn’t enough for a src
 
Do you know the run time to get hot for 12m of 22mm , and what size is best for the return in this situation?

I know 12m is about 4 litres, but I’m guessing you have to flow much more than 4litres through to replace all the cold with hot?
 
I would suspect on a domestic system that would run maybe 2 hours in a morning, 1 hour at lunch and maybe 2-4 hours at night it would be fine. In fact there's systems that I know of that are like this. I think the main issue is when it runs 24/7. But it's certainly an interesting topic as no manufacture can give you the main reasoning why.
 
Do you know the run time to get hot for 12m of 22mm , and what size is best for the return in this situation?

I know 12m is about 4 litres, but I’m guessing you have to flow much more than 4litres through to replace all the cold with hot?

0.11 per m for 15mm so 12m is around 1.4l

it all depends on your length as this needs to be replaced with hot / warm
 
Length is 12m, pipe is 22mm - so that’s about 4 litres.

So 15 mm return of 12 m too (another 1.4 litres)

So 5.5 litres of cold in pipes. Turn pump on, how much has to flow until pipes are hot . Presumably quite a lot more than 5.5 l, but how much?
Aldo what speed is secondary return pump run at? (Slow I guess?)
 
Normally around 1lpm max
 