I'm fitting a valliant eco tec plus 637 system boiler with a low loss header. Question 1, do my primary's in to the the header need to be the highest and lowest points with the secondary's teeing in between or doesn't it matter? Question 2, from the secondary flow they'll be a pump and then to a heating manifold for zoned heating circuits and then another secondary flow to a pump for zoned hot water. Do I need to put a bypass valve after the pumps and before the zone valve to each circuit and link in to the returns back to the header?

Obviously on a heat only boiler an external pump and bypass would be used but didn't no if this applies to a system boiler with an already built in pump and bypass but with additional pumps.

Some help would be much appreciated!
 
single boiler or multi boilers?

and flow to the top connection if your using the the vaillant llh the slightly lower top connection is for the boiler the higher one is the system

and any chance of a drawing o what your planning to do
 
It's a single boiler install with two hot water cylinders. I haven't actually got a valliant low loss header, but been told to make one. The system has 4 x underfloor heating manifolds and 2 x towel rail circuits.

IMG_9842.JPG
 
Looks fine to me just using two pumps

The only thing I would change is your flow for the cylinders put it above the boiler flow tapping where's your expansion vessel?

Also I wouldn't make a llh there cheap enough under a ton normally
 
yeah I meant to draw it with the boiler tapping below the two secondary flows. I've also been told that the boiler tapping has to be the top one then the two secondary's below and vice versa with the returns?

I haven't drawn vessel on here but was going to tee in to the primary return

Would you put bypass valves in after the pumps?

I would personally prefer a pre made llh been been told I have to make one!
 
it doesnt matter that much prefer the load higher than the supply

vessel and drain normally on the bottom of the llh
 
Cheers for your help

What about bypass valves?

i would normally install them on the end of the manifold but where you have drawn them is fine
 
Status
Not open for further replies.

Reply to SystemLow loss header in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
413
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock