Scenario:

Service/Cp12.

Tightness test, E6 meter with boiler and cooker.
1 mb drop found over 2 mins no smell of gas.
Acceptable drop.
Disconnected cooker, re-tested.
2 mins no drop.
Would you turn cooker off?
Or re-connect and just record the drop on the CP12 in the TT section.
 
re connect and note on cp its in limits
 
I thought that if you found an acceptable drop on tightness test an no smell then just noted down,unless advised to investigate from customer.Once you’ve gone to isolating/disconnecting appliances you’ve then got to cap the supply an make sure no drop? I’d cap off supply to cooker personally an leave it up to them now you’ve proved it’s the cooker
 
Last edited:
Now you have found the leak you need to cap the cooker, you know its leaking gas so its ID. There was no requirement to trace the leak as it was in the permissible drop and no smell of gas.
 
Now you have found the leak you need to cap the cooker, you know its leaking gas so its ID. There was no requirement to trace the leak as it was in the permissible drop and no smell of gas.
That’s exactly what I thought. Because I had disconnected and found it to be dropping on the cooker. The permissible drop is alliances connected.
 
only the same as cus removing it and cleaning behind
 
Scenario:

Service/Cp12.

Tightness test, E6 meter with boiler and cooker.
1 mb drop found over 2 mins no smell of gas.
Acceptable drop.
Disconnected cooker, re-tested.
2 mins no drop.
Would you turn cooker off?
Or re-connect and just record the drop on the CP12 in the TT section.

Why on earth did you bother. You can normally leave 8mb on an E6. Note the reading, move on. Don't give your punters unnecessary grief and urgent expense.

Frankly, if I had hired you, it would be the last time. And I would be asking questions.
 
only the same as cus removing it and cleaning behind

Not at all. A customer removing a cooker via the bayonet and reconnecting totally oblivious to the fact that it is passing gas is one scenario. A trained professional with a duty of care to the safety of his customer knowingly leaving a leak/dangerous appliance connected to the supply and not following the unsafe procedures act is another.
 
It was my understanding that a TT is not a legal requirement when doing a CP12, provision is made on the cert but its not a requirement but we all do it !
 