I would class it as an new install but with appliances connected
Cookers are notorious for small drops
thanks for your response
[automerge]1587307129[/automerge]
You would need to test this on pipework only as others have said.
There should be no drop on domestic pipework only whether existing or not.
If there is no isolation on the Boiler then one should be installed. It should have one and you need one to continue the test correctly.
If you have a drop, you cannot correctly assess whether the ECV is passing unless you disconnect and use a cap and test point directly on the valve itself. You also cannot be certain how big the drop is until you have proved the ECV is good.
so if you was to tightness test a job you haven’t worked on. During the let by test there is a drop. You then test for tightness on an e6 and it drops 1mbar over 2 minutes and pipework not all accessible and appliances not all with iso valves. Would you deem it unsafe
[automerge]1587307300[/automerge]
Appreciate the feedback. We used a full can of leak detector on all the new joints (probably about 15 in total) over and over again. And nothing. Not even a slight bubble. The engineer was happy that it was in the safe limit. But for some reason he was checking.
Would you guys walk away from that or not?
also is it possible rocol leak detector wouldn’t pick it up? is there a good gas sniffer on the market that’s reasonably priced and more reliable than ldf. Thanks