Hey everyone!

I have a towel warmer that used to work fine for a few months then all of the sudden stopped. As far as I can tell nothing has changed as in nobody fiddled with the balance of the radiators, the pressure in the combi boiler has been fine, etc.

So far I have tried:

  • bleeding the towel warmer - water coming out straight away, no trapped air by the looks of it
  • bleeding out a few cups of water and topping up to the right pressure
  • turning off all the radiators except for the towel warmer and turning the heating on
  • checked the thermostat valve and the little metal knob inside moves fine when pressed down
  • the pressure in the system seems to be dropping after bleeding the towel warmer
  • the pipe leading to the thermostat valve does not feel warm at all
  • all the other radiators seem to be working absolutely fine

Is there anything else I could try? I am completely baffled as to why it stopped working all of the sudden and none of the above helped :(

20210128_175121.jpg


20210128_175125.jpg


20210128_175136.jpg
 
Undo the trv head eg the bit you adjust there should be a pin does this move in and out when you push it in
 
The right hand one is lock shield remove nut on front and underneath is is a brass valve with Allen key slot make sure it is out
 
As Gasmk1 said but count your anticlockwise turns, and put it back to same position all but 1/4 turn.
Or you could try just hitting it with a spanner a few times (not joking)
 
I tried unscrewing it so it's almost level with the top edge of the valve, but it didn't seem to make any difference :(

Also tried the spanner hitting option, no luck either.

20210129_111151.jpg
 
If lock shield is open then it’s most likely to be a stuck pin on the trv- remove the head and waggle the pin in and out a few times.
 
Ok if you tried all of that I think it’s time to take the rad off and flush/inspect it outside with a hosepipe.

Open valves and see if water flows out nicely.

Connect valves together and see if you get flow .

Then report back
 
Did that as well, the pin seems to be moving freely
If you mean you can easily push / pull the pin in and out then that suggests that the valve has seized shut. The valve should normally be held open by a spring and considerable force should be needed to push the pin in.

TRVs often seize in this manner if they are left closed for longish periods, e.g. during the summer months. A smart tap on the pin with a small hammer may well free it but TBH, once they've seized once they seem to do so again and eventually need replacing.
 
Agree with Chuck
Tap with tack-hammer (or spanner) untill it springs back up. Would have said before but I've already used the hit it advice and didn't want you thinking thats all I could do😄.
I'd go as far as advising not to ever pull on the pin!
There's lots of ways to check flow and flush pipes and Ben-gee's advice is good.
 

Reply to Towel warmer staying cold after working initially in the USA area at PlumbersForums.net

Similar plumbing topics

I have just moved into a late 1990s new-build house with a small bore (about 1/2" OD pipes) gas fired boiler central heating system. All the...
Replies
4
Views
524
I have a caravan with a brand new heating system.The Valliant combi boiler is working fine but one radiator and one towel rail are stone cold.I...
Replies
1
Views
475
I've recently replaced an immersion heater for a direct cylinder, for 2.75-3kW. The new one seemed to be working a week before I got a callback. I...
Replies
5
Views
241
Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed...
Replies
1
Views
281
Hi everyone, About a year ago we moved into a new property which has a towel heater as part of the Central Heating System. There are no...
Replies
2
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock