Hi Everyone, I’m new to this site so not quite sure how it all works or if this is even in the right place but here goes.

I live in a large property that used to be one of the training centers for Lucas Engineering. However it has since been converted back to a residential dwelling.
The house has a single pipe system with very large pipe work and 42, 4 column cast iron ideal radiators. We used to have an old ideal floor mount boiler (I think 70kw). We have since upgraded it to a vailliant ecotec 64kw and made it a pressurized system along with a 80l expansion vessel.
We are having problems maintaining the right pressure.
When the heating is off the boiler reads 1bar, the second it turns on and the big external pump kicks in it jumps to 1.5bar and stays there. When left at this the majority of the radiators work fine but around 8 or 10 don’t come on until the pressure is increased to around 1.8bar at the boiler. And we seem to have to top this up most days. The plumbers who installed the new boiler just don’t want to know and won’t come back, we’ve had a couple other people out but no one seems to know much about this type of system.
There seems to be no sign of leaks as most of the pipe work is surface mounted.
Could the expansion vessel pressure need to be increased?
Any advice would be greatly appreciated.
Thank you.
 
When the heating is off the boiler reads 1bar, the second it turns on and the big external pump kicks in it jumps to 1.5bar and stays there. When left at this the majority of the radiators work fine but around 8 or 10 don’t come on until the pressure is increased to around 1.8bar at the boiler.
If you need to top it up daily, it's leaking somewhere you just haven't found where yet.

I'll be surprised if a heating engineer used to 'commercial' systems would have much difficulty sorting you out. Domestic installers are allowed to go up to 70kW but most of their experience will be with systems that are rather smaller. If you used the latter for the work you may find switching to another firm who domore of this sort of work is the easiest solution.

Anyway, to get the ball rolling, can you provide a diagram showing where the various components and pumps are located with respect to each other, please? Also a few photographs of the installation are always helpful.
 
@John.g do I remember you saying about the cgarge of a vessel being able to boost the pressure of circulated water slightly if increased? You're pretty good at this and I have no practical experience with commercial systems.
 
Hi guys,
Thank you for your replies. As for topping the system up I only do it every night to get the remaining few radiators hot, however if I don’t top up the pressure won’t go any lower so I’m not sure about leaks.
I was looking into expansion vessel sizing and I’m not sure if I’ve worked it out correctly. The boiler says there is 5200 lites of water per min in circulation, is 80l big enough? The boiler is located in the cellar and the house is three storeys with a large 4 inch heating pipe going all the way up into the loft so I would say there’s around 12m of head.
I will attach some photos for you to see.
Thanks again.
 

Attachments

  • D26F2FC9-0293-4BB9-BC09-9C3E2A4C456E.jpeg
    D26F2FC9-0293-4BB9-BC09-9C3E2A4C456E.jpeg
    99.8 KB · Views: 24
  • 5D48F146-B3C4-4ECF-9ADB-2D8002ABD370.jpeg
    5D48F146-B3C4-4ECF-9ADB-2D8002ABD370.jpeg
    144.4 KB · Views: 24
  • 36F10911-9A6E-4EEC-A726-BBC37997FC67.jpeg
    36F10911-9A6E-4EEC-A726-BBC37997FC67.jpeg
    104.9 KB · Views: 21
  • 8D91F894-4BFB-4E87-8944-20444B430030.jpeg
    8D91F894-4BFB-4E87-8944-20444B430030.jpeg
    106.5 KB · Views: 23
  • 1F423297-7CB7-4435-BDD8-E2C4C824BE40.jpeg
    1F423297-7CB7-4435-BDD8-E2C4C824BE40.jpeg
    140.4 KB · Views: 22
Sounds like the expansion vessel is slightly low on pre charge / not charged to system pressure
 
Obviously I have not seen the system you have but if the main heating pump can effect the boilers, you need to separate things, either with a header of some sort or a plate heat exchanger. The external pump will only cause problems if it isn't already.
The loss of pressure is a leak or loss via other means but needs finding.
Vessel (rough wild guess) 200 gal system? Haven't seen it but I am imagining a building the size of approx 8 typical 3-4 bed family homes if that helps you any?

First job, header or plate in my opinion.
 
The expansion vessel is sized based on system volume and the temperatures the system reached. If you go into real detail then one would use minimum system pressure, maximum system pressure etc etc as well.
 
Obviously I have not seen the system you have but if the main heating pump can effect the boilers, you need to separate things, either with a header of some sort or a plate heat exchanger. The external pump will only cause problems if it isn't already.
The loss of pressure is a leak or loss via other means but needs finding.
Vessel (rough wild guess) 200 gal system? Haven't seen it but I am imagining a building the size of approx 8 typical 3-4 bed family homes if that helps you any?

First job, header or plate in my opinion.

Thank you for your reply.
It’s a large 10 bedroom house.
42 of the big 4 column radiators that weigh a tonne!
A header plate was installed to start off with but the plumbers uninstalled it as the heating wasn’t working at all. But I think back then they were too scared to increase the pressure to anything above 1 bar with it being such an old one pipe system.
 

Reply to Trouble with single pipe system in the Commercial and Industrial Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
399
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
501
losing pressure
L
Hi all not a plumber but am an engineer I have pressure drop in the system Worcester Bosch came back after repressureising the expansion vessel...
Replies
2
Views
507
hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn...
Replies
5
Views
719
  • Question
Hi All I have a single pipe central heating system which was extended 20 years ago when we had an extension. The heating upstairs has never been...
Replies
8
Views
2K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock