Hi, Hopefully someone can throw some light on if this is a real issue or not.

I have had this boiler for about 10 years, I noticed just recently that when the CH has been turned off that a couple of the rads closest to the boiler were slightly warm. When the boiler had demand to heat the DHW I felt all the flow and returns and discovered the CH flow pipe was hot.

From looking at the boiler the DHW and CH copper pipes inside the boiler are teed together so the 3-way valve had to be on the return, from what I can see there is a small stepper motor that actuates an arm which is moving the valve, however the valve itself is all part of the Grundfos pump housing and that looks like a right nightmare to replace.

What I would like to please know is:-
1. Is the hot CH flow pipe normal or not? I guess not as it's a waste of energy.
2. Is there any possibility the issue lies with the stepper motor or the base and actuator the stepper mounts too and not the actual valve in the pump housing?
3. Can the travel of the stepper motor be adjusted in firmware to move the valve more tightly closed or not?
4. If it is the valve in the pump housing is it a pig to replace and best to put up with the slight loss of performance until it gets bad?

I have not tested to see when there is only a demand for CH if the flow to the cylinder DHW gets hot but I am guessing if it does then whatever is deemed here will also cure that.

Thanks in advance
 

Reply to Viessmann 200-w B2HA-35. CH flow pipe hot when only demand for DHW in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
285
MartinPod81
M
Morning, I have a job later this week with the above , Viessmann Vitodens System boiler. It has a 4 pipe setup with internal diverter and at...
Replies
4
Views
537
Hello all, I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring...
Replies
11
Views
1K
Hello, I am about to get the attached Viessmann 100-w heat only boiler with pump and diverter valve. Current boiler - Non Condensing System - OV...
Replies
2
Views
722
Hi guys. A couple of things. 1 am I better fabricating bends in 14 mm copper for my ch or are 90 degree elbows fine, ref flow, friction ect. 2...
Replies
0
Views
309
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock