Discuss Viessmann Vitodens 100-w configuration with Nest in the Central Heating Forum area at PlumbersForums.net

Messages
2
Hi all,
I had a new Viessmann Vitodens 100-w boiler (the new version) installed last year. The guy who was installing and commissioning it had never seen or commissioned this boiler before, so I guess he didn't do it in the most efficient way:
1. I've got Google Nest thermostat but it looks to be connected as a regular switch on/off thermostat - not in Opentherm mode.
2. The boiler display and Vicare app always show that Heating circuit 1 is off. But the boiler does switch on when Nest wants so. If I switch on Heating circuit in the boiler, it starts working based on the Vicare app schedule.
2. Flow temperature gets to 70 when triggered by Nest. Adjustment of regular/comfort/reduced flow temp in the Heating circuit doesn't change anything (well, probably because the boiler thinks the Heating circuit is Off all the time).
So my guess is that the installer connected the Nest as an external heating demand trigger. I went to parameters menu and changed "Flow temperature for External demand" from 70 to 55 - it helped, and now Flow sets around 55 when triggered by Nest.

I want the boiler to be as efficient as possible. The question I have now is - can I do something with the configuration myself to make it more efficient (I don't know if weather compensation is enabled at all, for ex), or shall I invite an engineer who can reconfigure it to work with Nest via Opentherm (dynamic flow temp change, etc)?

Any advice?
 
I've had a viessmann 100-w with Nest for 3 years. The Nest is connected via the opentherm connections so it can modulate the boiler. I spoke to viessmann and they said you can't have both Nest installed on opentherm and the outside temperature sensor installed, (so I didn't install the temp sensor).
 
I've had a viessmann 100-w with Nest for 3 years. The Nest is connected via the opentherm connections so it can modulate the boiler. I spoke to viessmann and they said you can't have both Nest installed on opentherm and the outside temperature sensor installed, (so I didn't install the temp sensor).
Thanks, this is really helpful. Has it been useful or more efficient to have the connection via opentherm?
 

Reply to Viessmann Vitodens 100-w configuration with Nest in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

    • Like
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few...
Replies
1
Views
1K
Morning, I have a job later this week with the above , Viessmann Vitodens System boiler. It has a 4 pipe setup with internal diverter and at...
Replies
4
Views
537
D
hello! while saving up for a new plumbing and heating installation for my new one bedroom flat, i did a lot of research on different boilers and...
2 3 4 5 6
Replies
51
Views
4K
Hello I have a NEST with Viessmann system boiler with unvented cylinder. I have a mid position and two position valve I thought the mid...
Replies
1
Views
785
Hello, I am about to get the attached Viessmann 100-w heat only boiler with pump and diverter valve. Current boiler - Non Condensing System - OV...
Replies
2
Views
721
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock