Discuss Worcester G* Cdi 37kw... Luke warm DHW in the Gas Engineers Forum area at PlumbersForums.net
Hobo128
Hi guys...
Happy New year to you all....
Been out to a Worcester Greenstar Combi last week.... Problems with hot water not getting very hot.... Boiler is set to max on and I'm getting about 40 degree out of the tap.... Turned of the flow and return at the boiler to check diverter but this made no difference.... Should I change the plate to plate.... Thanks
Your return temp back to the heat exchanger (boiler)
should be at the same temp as your hot water out
Sorted it.... Flow rate was to high and also burner was very dirty... fan pressure test proved this.... Cleaned it and adjusted the flow rate.... seemed to sort it... thanks
Reply to Worcester G* Cdi 37kw... Luke warm DHW in the Gas Engineers Forum area at PlumbersForums.net
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...