Ok so I called gassafe today to check hoe to clasify low working pressure and was told if it's not effecting combustion then just note it as a fault (ncs) if it is then it's AR.
I've always worked on the principle that when it's close to 14mb or below I'd put it AR and if it was badly effecting combustion ID.
My principle being that possible explosive start-ups and corrosion caused by poor combustion are potentially dangerous and that 14mb is just too low not to take seriously.

Apparently I have no leg to stand on but I still disagree!?

What's your oppinion?
 
Some boilers can run at as low as 14mb and still work fine without performance issues. All I would do is test its safety and follow manufactures guidance. Take evidence of readings and make note of the issue and present it to the customer letting them know of possible effects.

It could be 14mb when you test it but what happens during high demands, that will lower it even more. Also with other gas appliances running it will lower it even more. I would personally AR it.

I don't agree but what gas safe says goes I guess.
 
A.R.
It's not going to miraculously get better.
Ultimately it's your call, not Gassafe.

As you are now, if you've found a boiler working at lower than normal pressure it's a judgement whether to leave it on.

However if you went to a boiler someone else had A.R'd with the same 14mb, I think it's most unlikely you, or any other GSR would put it back into service without fixing it.

What's the difference?
 
On the job that prompted my query the pressure is just over 14mb but it's clearly been piped in 15mm even tho boiler tail is 22mm and really wouldn't be hard to change, it's also one of many rentals that the customer owns so I'm going to stick to my guns this time.
 
14mb working is ok so long as it's maintained with other appliances working and also maintaining 1mb drop accross the installation pipework. Have you tested working at the meter?
 
1mb across installation I'm not bothered about (I didn't put it in) if it was less than 19 at the meter I'd consider calling transco (or whoever do it now).
It's 22mb dynamic at meter and piped in 15mm.
Granted 14mb is on gas valve so could be as much as 16mb before it, but it's still a crap job that needs putting right IMO
 
Ncs for me aslong as it’s running right
 
Your right I'm sure but would the fact that they replaced the hob burners with random ones from a different hob that rocked around and were clearly dangerous (in a rental property) maybe cause you to be a bit stingy with the rest of the installation too?
Obviously I made that safe...
 
This really depends on what you are measuring at the gas meter say if its 20mbar working pressure and 14 mbar at the boiler then the pipework is undersized , if its 18mbar or lower working pressure at the meter I would be getting cadent out to either tweak the regulator or replace it if necessary I personally would not leave 14mbar especially if there are other gas appliances Hob would be ID for me . Kop
 
I'm with you but it's not what gassafe say.
If it's not impacting on combustion it's 'officially' NCS and even if it is then only AR.
That's with other appliances running (3/4 hob etc)
I was a originally a commercial engineer and certainly wouldn't leave a big forced draught burner running at 14mb, but then you don't get so many cowboys undersizing pipe on commercial;)
 
Had one myself for a lettings agency boiler running at 15mb and 5 mb drop from meter. The boiler is under warranty and the Gas valve needed replacing but the wouldn't do it because it's not been installed to manufacturers instructions so it does matter .
 
Where are you measuring the 14mbar, I remember having an issue with a Vaillant ecotec pro, we were installing them on a council contract, Vaillant were convinced the gas pipework was to blame, it was 22mm from meter to boiler, only appliance in the property, the gas board could only get a maximum 19mbar working through regulator, I cut a test point into pipe at boiler and registered 19mbar working, at that point the Vaillant gas valves were fitted with a flexible hose from gas inlet and it was restricting the 5mbar didn’t here the outcome after that, you’ve already confirmed pipework is undersized so that’s got to be AR, any combustion problems and it’s ID, end of the day it’s been installed like that, I guarantee it’s not been commissioned and there’s no trace of who done it, your last in so you can only advise the necessary works to bring it up to standard and let them sign the warning notice, I wouldn’t take a voice conversation as legit even from gas safe I’d want it in writing, always cover yourself
 
I'm glad I've not got you servicing my boiler @Dake205, I still haven't put that loft ladder in:)
There’s always fine lines personally that’s more of a health and safety issue that a lazy engineer would use to justify not doing it, other problems require we have to jump up lofts or crawl under floors so why make an excuse when it comes to a boiler
 