Hi all wondered if someone could help me out with my question.

For a wile now I've had problems getting heat to the last radiator on the system at my house.
All the rads are now cast iron,in total I have 7 rads and a Myson plinth heater in the kitchen.

Being a plumber by trade I've tried everything that springs to mind to sort this out.
1. Tried throttling all the rads back to allow heat to the last rad which worked,it got hot but not banging like some of the others on the system.
2. I've spent hours balancing all the rads which works fine for all the other rads but after trying this the last rad goes cold again.
3. The whole central heating system was only installed 12 years ago so there's no valves that could be half shut or stuck on the last leg
4. I've power flushed the whole system every time I added a new rad so the systems clean.
5. I have traditional looking valves which are all working fine wheel head & lock shield.

I used to have a Radiant 28kw boiler only a cheap make then I swooped it out for an early Worcester Bosch greenstar 25 he the one that was discontinued in 2003 I think but this was old stock that was left on the shelf or a wile.
I had similar problems with my last boiler with the last rad not getting as hot as it should so I thought the replacement boiler would sort this but I'm thinking because I'm now running cast rads this is where the problem lies.

Ive totalled my but output of all the cast rads inc the plinth heater and it comes to 46000 btu which I thought the Bosch boiler would have been able to handle.?

Can someone advise me if it's just a case of a under powered boiler trying to run all these rads.

Thanks again all

Kev
 
46000 btu is only around 14kw. The size of the boiler isn't the problem.
 
46000 btu is only around 14kw. The size of the boiler isn't the problem.

Well just to add a little more info.

The last radiator on the landing before the affected radiator seems to air lock now annd again which in turn cuts the flow off to the affected radiaror abd I dont know why.

Cheers kev
 
How many rads do you have running off of 15mm pipe work?

Cherrs for the prompt reply.

All the rads are running off 15mm copper. The pipework hasn't been altered since a complete new install 12 years ago before that the house never had gas central heating just electric wall heaters.

Cheers
 
There you go. Can't get enough heat in 15mm to service all those rads properly.
 
There you go. Can't get enough heat in 15mm to service all those rads properly.

If that is the case would I have to replace all pipework or just the main flow and return that runs to the affected last rad.

Cheers for your prompt reply.

Cheers
 
Ideally you'll want 22mm f&r. Depending on the runs you may be able to get away replacing some and not all of the 15mm f&r.
 
Ideally you'll want 22mm f&r. Depending on the runs you may be able to get away replacing some and not all of the 15mm f&r.

I would think the run from the boiler to the last rad upstairs would be around 15mtrs long but I be right in saying it would be better to replace all the flow nd return pipework with 22mm.

Cheers
 
And would I be right to say the current boiler I have would be fine running 22mm pipework.

Thanks agin for your imput.

Yes, you really need 22 with individual 15 branches to rads. I've seen boilers really badly damaged by insufficient flow, so best get it sorted sooner rather than later.
 
Yes, you really need 22 with individual 15 branches to rads. I've seen boilers really badly damaged by insufficient flow, so best get it sorted sooner rather than later.

Hi so can I still run the flow and returns to the rads off the 22mm in 15mm as the longest run will only be about 15ft and it's the 3rd rad off the boiler and about 3ft on the first floor.

Cheers
 
Yes that would be ideal. I don't tend to run any more than 3 radiators off of 15mm copper depending on rad sizes. If you start from the boiler in 22mm and pipe as far as poss in 22mm then reduce down for the last couple. You should find the extra flow will resolve your problem.
 
Cheers guys for all your advise......just one more question. Would be best if I run the main flow and return pipe in 22mm all the way to the last rad then Reduce to 15mm for the valves. Then just tap off the 22mm and connect upto my existing 15mm legs to the rest of the rads.


Cheers
 
You'll be fine with the last rad on 15 f&r. It's basically a long tail.
 
Have you flushed your cast iron rads before installing them?
 
Status
Not open for further replies.

Reply to Sizing my new combi boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
128
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
451
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock