Hi folks,

New to the forum and a total noob. Please be patient :).

We're in the process of moving into a newly renovated house. One of the renovation jobs was the heating system. We've had an unvented Warmflow pressurised system installed along with new radiators. We've been without heat or any water for almost a month due to bit-part work from the plumber who has apparently been very busy.

We were assured weeks ago that the heating would be on. Thankfully we were able to get it back on last Thursday. The plumber left before the heating was back on and I got my electrician to connect the newly installed Nest 3rd Generation thermostat to the boiler.

The heating switches on OK and the thermostat will click on/off based on the selected temperature however, the hot water does not work.

If I select hot water boost from the Nest thermostat I can clearly hear the clicking noise that would lead me to believe it is working, but the Warmflow pressurised system doesn't appear to be heating anything.

Our plumber assured as when he left that this would all work no problem. What is going on here? Is it something simple? The hineysell 2 port valve just stays at auto. Is it supposed to move when hot water is engaged? The plumber did mention something about a valve in the attic. I wonder is this left closed maybe? He said the Nest thermostat should open any closed valves.

I've attached a few photos of the install. If I'm right, the valve to release air/steam is connected to a pipe which points to the ground. This means water would just empty on the floor. I thought this was supposed to release somewhere outside the building? Appreciate any help you can provide. Our plumber said he won't be back until next Wednesday to finish off one or two things. Could really do with this on ASAP as we were looking to fully move in any day now. Its been well over a month now. Thanks all!

20171210_121720.jpg


20171210_121725.jpg


20171210_121754.jpg


20171210_121811.jpg


20171210_121833.jpg
 
yes that pipe must be run outside of the building also should have Tundish fitted so you can see if the valves are passing due to fault conditions, the honeywell valve should move to open when there is a call for hot water you can tell if it is open by the handle on the end will have no restriction when no call the valve will close and you can feel the restriction. the other valve in the loft is probably the honeywell valve for the heating, which he will have opend and locked in manual to fill the system. if you still have no hot water you could try the immersion heater on th cylinder. looking at the photo this is the switch next to the isolator but get it checked as that should be fused also.
 
  • Like
Reactions: G M
That's an absolute mess, bet the plumber isn't G3 registered

Did he install the boiler ?

Any chance of a few pics of the boiler ??

Also your electrics are a mess and need sorting out
 
That's an absolute mess, bet the plumber isn't G3 registered

Did he install the boiler ?

Any chance of a few pics of the boiler ??

Also your electrics are a mess and need sorting out

Hi,

No, the boiler is in the garage and it's about 10 years old. The burner also needs replaced. It is from the 90's. We're getting these replaced after Christmas along with the tank being moved. It is car too close to the house.

Wouldn't know of the plumber is G3 registered or not. Could the pipes not have been tidied away a lot better than they are?

Another real concern I have is that pipes were tracked through the concrete flooring and the water wasn't switched on until after these were filled in. There could be a leak. The problem here is that, because of the repeated delays with the plumber, the other tradesmen we had lined up to do the floors had to go ahead and fit them. Delays can caused all sorts of issues. When you're told a 'million percent' that the heating and water will be on by a certain date, you'd think that would be confident enough to organise the other jobs but typically, this wasn't completed in time.

What electrics need sorting out? Compared the the pipes I don't think it looks too bad. Thank you!
 
yes that pipe must be run outside of the building also should have Tundish fitted so you can see if the valves are passing due to fault conditions, the honeywell valve should move to open when there is a call for hot water you can tell if it is open by the handle on the end will have no restriction when no call the valve will close and you can feel the restriction. the other valve in the loft is probably the honeywell valve for the heating, which he will have opend and locked in manual to fill the system. if you still have no hot water you could try the immersion heater on th cylinder. looking at the photo this is the switch next to the isolator but get it checked as that should be fused also.

Hi,

Thanks for the reply. The valve doesn't appear to do anything when the hot water is switched on. I can hear the clicking noise when selecting hot water but no activity whatsoever from the pressurised system or the Honeywell valve. If I move it manually to the right it sounds like water is passing, then the lever slowly moves back into the auto position.

Thanks!
 
you can lock the valve open temporary if you look at the valve pull the lever fullly open and liftit slightly and let it nestle into the recess you will get hot water while the heating is calling
 
  • Like
Reactions: G M
Hi,

No, the boiler is in the garage and it's about 10 years old. The burner also needs replaced. It is from the 90's. We're getting these replaced after Christmas along with the tank being moved. It is car too close to the house.

Wouldn't know of the plumber is G3 registered or not. Could the pipes not have been tidied away a lot better than they are?

Another real concern I have is that pipes were tracked through the concrete flooring and the water wasn't switched on until after these were filled in. There could be a leak. The problem here is that, because of the repeated delays with the plumber, the other tradesmen we had lined up to do the floors had to go ahead and fit them. Delays can caused all sorts of issues. When you're told a 'million percent' that the heating and water will be on by a certain date, you'd think that would be confident enough to organise the other jobs but typically, this wasn't completed in time.

What electrics need sorting out? Compared the the pipes I don't think it looks too bad. Thank you!

You need to check he has his G3 else he can't / shouldn't of fitted your unvented water cylinder

We're the pipes insulated/ protected from the screed ?? Or was it just bare copper pipes in the floor

No grommets used clips fixings etc

Bet if you look at the left spur / switch you can poke your finger where the wire goes which is a big nonono

Also no protection where the cables enter the adaptable box
 
you can lock the valve open temporary if you look at the valve pull the lever fullly open and liftit slightly and let it nestle into the recess you will get hot water while the heating is calling

Thanks a lot for that. I've moved it over and locked it in the manual position. The system is making all sorted of stomach gargling noises. Maybe that's a good thing!

I've been told that if the gauge on this orange vessel thingy is too low then we might have a leak. Looks a little on the low side to me. Is this normal? See attached. Thanks again for the help. Really appreciate it!

20171210_155838.jpg


20171210_155855.jpg
 
You might

Do you even know if your old boiler is capable of being sealed most old ones arnt?
 
You might

Do you even know if your old boiler is capable of being sealed most old ones arnt?
Wouldn't know that but I've attached a picture of the boiler and burner. We're hopefully getting them replaced some time after Christmas. Thanks.

20171210_161536.jpg


20171210_161525.jpg
 
Is that the thermostat phial if it is I would be worried
I use a Nest smart thermostat which appears to be working correctly. Don't even know what that one on the boiler does but it's getting replaced soon anyway.

The hot water is working now. Thanks @Gasmk1 for your help! I suppose this means that either there is an issue with the way the Honeywell valve is wired up, or the valve itself is at fault. I don't think it's the, Nest Link thing as it seems to make a clicking noise when I turn hot water on, as if it's working. It's just the valve doesn't do anything.
 
I would say the wiring is at fault
 
  • Like
Reactions: G M
That's the fire valve capillary above the burner to cut off the oil in a fire. The blue bird does have a high limit stay.

Your 'plumber', and I use that term loosely, has made a bit of a pigs ear of that cylinder install. The combination valve will be fun to change. D1 looks too long and D2 and tundish are missing. If the safety valves let go then you could be flooded.

On the plus side, he didn't use a hotun
 
Hi @ShaunCorbs sorry I didn't reply to this earlier. You make some interesting points...

We're the pipes insulated/ protected from the screed ?? Or was it just bare copper pipes in the floor

Nope. No insulation whatsoever. He used plastic piping which goes across the floor. I've attached a photo of stuff used. Doesn't seem very durable. Is hot water OK to flow through that? More worryingly, over time this may move as it is installed across a walkway - between 2 radiators either side of a 2M opening to the kitchen. I'm not sure where else they're installed.

No grommets used clips fixings etc
Is this standard practice for an install like this? I don't see any grommets used. In addition, the hot water outlet is clearly leaking. See attached photo.

Bet if you look at the left spur / switch you can poke your finger where the wire goes which is a big nonono
Wish I knew what that was lol. I'll see if I can get someone who knows more about it to check. Thanks.

Also no protection where the cables enter the adaptable box
What kind of protection is needed for them? Just a cover? Thanks

20171210_165219.jpg


20171210_165148.jpg


20171210_170535.jpg
 
That's not good any heat in the pipe / from your hot water system is going to be heating the floor, it does look good so far

No and over time the wire could rub and fray leading to live wires on show
 
That's not good any heat in the pipe / from your hot water system is going to be heating the floor, it does look good so far
Does or doesn't look good? I'll take a guess and assume you mean doesn't!

There's a pipe with a termination type handle on the end just hanging there. Could this possibly be for the shower which is going to be plumbed in through the wall on the right? Not totally sure what this is for.

Sorry about all the questions, but believe me, I am learning a lot from all the replies, so thank you!

20171210_163135.jpg
 
Sorry but your right doesn't look good

And that point shouldn't be there as really that pipe is just for the expansion vessel
 
  • Like
Reactions: G M
Hi folks,

Sorry to reignite this thread. The heating system appears to at least be working ok since my last post however, one thing happened a few mornings ago that concerned me.

When the heat switched on as scheduled around 07:15 a few mornings ago, there was loud banging and knocking noises that appeared to be coming from the attic. From my bathroom I could hear the knocking noise clearly alongside a louder than usual sound of flowing water. It sounded like there was water being poured on the ceiling above me!

I checked the newly installed cylinder and noticed the gauge below the expansion vessel had dropped to zero. I turned the little tap which I believe allows water to flow into the system and switched it off again when the gauge got to around 1.5 bar. The system seems to be working ok and the gauge hasn't really dropped since this happened a few days ago. It is concerning that this happened and I'm not sure if something more serious would have happened if we weren't at home. Any ideas what may have caused this?

One final point. Should we not be getting an installation certificate of some kind? Thanks!
 
Not good can you get into the loft / where the noise was ?

Pressure should be a min 1 bar in the system

And yes both an unvented certificate and a building control certificate
 
  • Like
Reactions: G M
Not good can you get into the loft / where the noise was ?

Pressure should be a min 1 bar in the system

And yes both an unvented certificate and a building control certificate

Great thanks a lot. I'll grab a ladder and stick my head up to see what's going on.

Good point about the building control certificate too. I think they will most certainly have an issue with that emergency pipe or whatever it is that will just dump water on the floor. Our plumber said that a friend of hours said he would run the pipe outside but no one mentioned this to me at the time or I would have disputed it. It still isn't done.
 
I have a grundfoss ups2 that occasionally decides not to run. Wakes the street up. I have one in the van but waiting on landlord to sort it.
 
  • Funny
Reactions: G M
Thanks. I stuck my head up and thankfully no sign of any water or leaks. I just don't understand why the pressure dropped to zero and all the banging and knocking noises started. I guess there is just a lot of air in the system. Might bleed all the rads again. We've had to do that a few times already as some of them weren't heating that well. Thanks all for the fast replies!
 
Boiler is in garage but noise resonates through pipework and can give a false signal as to where the noise is actually coming from.
 
  • Like
Reactions: G M
Hi folks, several months on and the heating system seems to be behaving itself now. The needle hasn't budged below 1 which is a good sign I guess. Only thing we notice now is a knocking noise coming from the pipes (I think) in the ceiling. This happens every 10-20 mins or so 24 hours a day. It's a little annoying and is less noticeable since we got the loft insulation installed. Any ideas what this might be? Thank you!
 
Are the said pipes in the loft ?
 
  • Agree
Reactions: G M

I would say the insulation is pushing down on the plastic pipe causing it to be touching the joists / rafters and thus causing your noise

They need clipping
 
  • Like
Reactions: G M
I would say the insulation is pushing down on the plastic pipe causing it to be touching the joists / rafters and thus causing your noise

They need clipping

Thanks. The noise was there before the insulation was put in but I think you're correct. None of the pipes appeared to be clipped down. At least when I was in the loft I didn't see them clipped anywhere. I may have to have another look. Would have expected this done as part of the heating system install mind. Thanks for your help!
 
Status
Not open for further replies.

Reply to No Hot Water after Heating Switch-on in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
129
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
280
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
293
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
119