Hi,

My existing system boiler if fed via a fused connection unit off the ring final circuit, when the boiler is replaced is it a requirement/best practice, that the boiler is fed via a dedicated circuit from the consumer unit to the fused connection unit.

Cheers

Ian
 
its fine off the ring/ as it its
 
Hi,

My existing system boiler if fed via a fused connection unit off the ring final circuit, when the boiler is replaced is it a requirement/best practice, that the boiler is fed via a dedicated circuit from the consumer unit to the fused connection unit.

Cheers

Ian

Contributing as spark .............. no

Why do you ask
 
Leaving it on the ring circuit is not "Best Practice". A dedictated circuit is.

Thanks to the forum I now know is not an 'electrical' requirement, is the dedicated circuit preferred by plumbing professional trade bodies as best practice
 
Nope aslong as there's a fused spur it doesn't matter a feed could even be taken off the lighting circuit if acceptable (loading etc)
 
If you are having an electric boiler fitted, yes a dedicated circuit would be required ...but for a gas boiler absolutely not a requirement.

I may be wrong but an elec boiler rated at 3kw should be fine ?
 
Hum.... I wouldn't, sure if it had a 13A plug on it but anything with a load above 2 Kw should be on its own circuit

would a fcu be acceptable ? just thinking of those 3kw wall/panel heaters
 
Thanks guys for the clarity, in my case it is a gas fuelled system boiler, electrically everything is fine, so I’ll leave it as is, I just didn’t want to fall foul if some other requirement I wasn’t aware of that I could sort in advance.
 
A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.

thats ok if the system is rcbo but if its on a split board half of its going off when the rcd trips any way
 
A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.

There are no regulations that state this ....

But there are regulations about spurs off spurs, which plumbers tend to ignore.
 
  • Disagree
Reactions: Vee
There are no regulations that state this ..

But there are regulations about spurs off spurs, which plumbers tend to ignore.

Vee- you can disagree with me you like, but please offer up a BS 7671 reg number to back up your position
 
You are missing the point as this is not about regulations, but what is correct for a particular scenario. You are generalising for a boiler.
 
You are missing the point as this is not about regulations, but what is correct for a particular scenario. You are generalising for a boiler.

Err no.

I am offering a direct answer to the op.

His question was do I need a dedicated fused spur for a new gas boiler.

The answer is no.
 
There are no regulations that state this ..

But there are regulations about spurs off spurs, which plumbers tend to ignore.
Equally electricans often fail to understand controls.
Err no.

I am offering a direct answer to the op.

His question was do I need a dedicated fused spur for a new gas boiler.

The answer is no.
He asked about Best Practice, not just the minimum requirement under the Regs. Surely that can differ?
 
A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.
Murdock - You surely understand what I am saying her and if you where so up on your Regs you would not disagree with this. Have we touched a nerve?
 
Not touched a nerve ... Just making sure an unsuspecting client isn't badly advised by a plumber, regarding electrical regulations.

It's that simple.
 
  • Dislike
Reactions: Vee
Not touched a nerve . Just making sure an unsuspecting client isn't badly advised by a plumber, regarding electrical regulations.

It's that simple.
What makes you think you are the only electrician on here?
 
I am an electrician and install boilers.. lol
No requirement as Murdoch says but if it was my house, it was easy, and i had a RCBO board, then definitly i would give it a dedicated cct.
Boilers often have zone valves, boilers also often leak, when i am fault finding a tripping RCD, boilers like outside lights and outside sockets are well up there as potential culprits. Having a dedicated cct just makes it easier to find and reduce the nuisance factor
 
Personally, I would like to see the boiler on a dedicated RCBO, if it were a new installation in my own house.

I have lived in places where trivial faults on a heating system (normally a room stat, weirdly) have tended to trip the RCD, and it nice to be able to pinpoint the cause more easily. That said, where I live at present, the fused spur is off the ring main and it has not caused any trouble in the last two years and I have no intention of having a new circuit installed at the present moment.

Thinking to the last time I read the electrical regulations (not that I am an electrician), I think there was some point made about the advisability of designing a system to avoid nuisance tripping, but I think this was to be interpreted by the designer of the installation. As you are not installing an entire new electrical system, I doubt you would be expected to have a dedicated circuit for a replacement gas boiler, but I expect some people will disagree: if there's one thing I have learnt about electricians, it is that no two will agree on everything.
 
I don't, but I'd hazard a guess that if it's for a whole house the heat requirement is well above 3kW :)
I appreciate your logic and your quite right I would guess a whole house is above 3Kw. A jobwe did recently did surprise myself I had to double check my calcs.
A barn conversion with heat pump in mind from the beginning. The total heat loss for 3 bed, 2 en-suite, lounge dinner, large kitchen etc. etc. was just 4.2 Kw. It cost a few quid and there was plenty of non standard work but shows things can be done very well when the money is there. Sorry to hijack the post
 
Status
Not open for further replies.

Reply to Dedicated circuit for Boiler Power in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
270
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
491
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the sink, dishwasher, washing machine etc. When I pour the concrete there won't be any chance to dig it up anymore. From my own research I get the...
Replies
0
Views
137
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
359
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
257
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock