Jim Goodenough

Esteemed
Plumber
Messages
653
I have a customer who wants an unvented HWS, they have a Aqualisa Quartz Gravity Pumped QZD.A2.EV.14 Shower which has a max pressure of 1 bar.

My question is if I fitted PRV's set at 1 bar, on both H & C services to the shower pump once the UVHWS system is installed, would this be sufficient for the shower to operate normally?

MTIA
 
Nope time for a new shower if they don't do the high pressure box / control unit
 
FYI, I've contacted Aqualisa and they say I need "our mains compatible HP processor valve which will be half the size of your existing. They can take up to 7 bar of working pressure and are available at a cost of £302.99 including VAT, plus £2.95 for the postage and packaging"
 
Status
Not open for further replies.

Reply to Aqualisa Quartz Gravity Pumped QZD.A2.EV.14 Shower in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
197
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
114
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
443
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock