Discuss boiler locks out , complete service and parts change in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net
new cell fitted and still the same , chamber all cleaned, new nozzle and good sparkI’m not an oily, but if it works when you apply light, I’d be looking in that area. Either faulty photo cell or not enough light?
grant vortex 16/21 riello burnerYep, give us an idea of the boiler and burner.
Need a new boiler man as well if they're stuck with this.
cell works exaclty as it should when out but locks out everytime when in position grant vortex 16/21 riello burnerMight be seeing a false flame, to test, keep light shining on the removed photocell before trying to fire up, it should lockout and not fire up.
Make of boiler/burner?.
cant answer that has boiler man has given up and leftWhat co2 and excess air is it running at?
grant helpline say its a combustion issue but when we trick it to go it burns well fires up lovely and runs finegrant vortex 16/21 riello burner
Reply to boiler locks out , complete service and parts change in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.