Discuss Boiler Return Temperature Control in the Central Heating Forum area at PlumbersForums.net

John.g

Esteemed
Plumber
Subscribed
Messages
3,977
I have rarely if ever seen mention of this form of control being used, which Valliant, for one, have available for years, is there a reason for this?
 
I wasn’t aware of this, I’m guessing the need is for lower temperatures required for commissioning? Vaillant Ecotec Pro has flow and return temperature accessible via the diagnostic menu, which others may too?
 
If you used 'return temperature' directly as the primary form of control, the long time-lag between changing the boiler output and seeing a response on the return temperature would result in a system that is unstable, i.e. the boiler would short-cycle.

Modern domestic boilers often do, however, modulate to keep the difference between the flow and return temperatures to a fixed amount, e.g. 20degC subject to not exceeding the specified maximum flow temperature. They may also wrap the primary control loop in a secondary control loop that monitors return temperature to ensure that condensing occurs when possible. The algorithms used are proprietory so you need to be pretty determined (and have a data-logger and some thermocouples) to figure out exactly what strategies are being used by a given manufacturer.
 
Last edited:
I don't think the control is direct as someone on here (Vaillant Ecotec 418) briefly c/o to Return Temp control, it had been set to Flow control with a SP of 70C which gave a return temp of 55C, the target temp was then set to 55C on c/o and the flow/return temps then fell to 47C/37C, with a observed d.05 of 36C which is the "Determined heating flow set target temperature", presumably, this was now the calculated return temperature required?. Unfortunately, as there were more pressing problems at the time, the test was not continued, maybe there's a volunteer or two out there?.
 

Reply to Boiler Return Temperature Control in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
169
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
325
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
192
Hi all, this is probably a daft question but I need to run my cold feed from one side of my wall mounted boiler to the other. Running it beneath...
Replies
2
Views
219
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could...
Replies
0
Views
271

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock