Discuss Bosch junior 28i pressure goes up and down. Advice please. in the Central Heating Forum area at PlumbersForums.net

Messages
6
Hi.

After the issue, I've had recently and a visit from an engineer (full story below) I've got the following symptoms. On my boiler Bosch, junior 28i pressure goes all the way down to 0 bar when only hot water is in use but goes all the way up to 3 bar (and probably above) when central heating is on. Hot water has no effect on the pressure even when it's high. I don't want to use that company/engineer anymore, even though I'll not pay anything (insurance). I've spent most of today on educating myself, and for me, it looks like it might be a faulty expansion vessel. I'm an electric engineer so I need help with this one. I want to get some opinions from more qualified peoples before I'll call someone locally to do a proper repair.

Full story here:
About two weeks ago my PRV blew off when my wife tried to switch the central heating on. I've called my insurance provider who managed to get a gas engineer the next day. Came in said I need a new PRV and someone will replace it within a couple of days. He also increased the pressure and said it's ok to use the boiler as usual and do not worry about leaking water outside. Boiler died 3-4 hours after his visit, so I rang them again the next day, and after 5 appointments that no one turned up, hours on the phone, and 10 days without heating or hot water he finally came back. Changed PRV switched the heating on, showed me that's working, and quickly left. I've asked him a couple of times did he check for a cause of the blown PRV, but he said everything else is fine. When he left pressure was about 1.5 bar 10 minutes later it was just under 3 bar and I've switched the heating off. I've called his call center again, but they told me they can't do anything because when the engineer left my property I've had hot water and central heating. If I want them back I need to leave the heating on and let the PRV blew off again.

At the moment I can switch the heating on for about 10-15 min and leave it off for about 1.5h. That's the time for the pressure to go from 0 to 2 bar and back to 0 again.

I really appreciate any help.
 
yep sounds like expansion vessel has gone either needs re charging or if split needs changing
 
yep sounds like expansion vessel has gone either needs re charging or if split needs changing

Thank you.

I feel like the engineer that came to my house work for himself (no company uniform or van), and because it's going through insurance, I've got no option who's coming over, hence he don't care how many times he'll have to come back and fix it as he got paid for every visit.

I'll keep this thread updated.
 
Probably didn't want to take the boiler off the wall to replace the expansion vessel. Absolute bag of shiyte boilers to work on!
 
According to the manual if there's over 340mm clearance above you can slide it upwards without touching the boiler itself, and there's nearly 450mm clearance on mine. Access is a bit awkward, but I think he just wanted more of my insurance money. What would be a reasonable cost to exchange the vessel and do a boiler service in the Wolverhampton area.? And if there's anything else that I should ask to check or replace? I'll get some quotes after the weekend. Thanks for help.
 

Reply to Bosch junior 28i pressure goes up and down. Advice please. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
505
losing pressure
L
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
606
the pressure of my boiler looks unstable After i re-pressurize to 1.5 bar, using tap is ok without problem. but when turn on the central heating...
Replies
0
Views
412
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
273
Hi, Boiler is losing pressure, from 1.5 bar to 0 bar in about 4 hours. Have checked all rads and seem to be fine, no water out external prv...
Replies
5
Views
653