got a test and purge tomorrow so have to read up tonight on butterfly valves not sure if there allowed or not anybody know the answer off the top of there head its a bula gasket forming the seal on the flanges
 
tomorrow I can find the guy who ordered it find some sort of delivery info and find the manu I can also find six numbers and marry shakira which is more likely and doesn't involve some stupid git saying I got from bss I think the strand of thought I have concerns seals on gas valves used as ecv,s
 
Short of actually removing and inspecting it just do a let by downstream of it.
 
If it has epdm seals you cannot use it on gas
 
TA valves will have a sticker with Nitril if its for gas.
 
had to look in igem up2 and the boss catalogue it is a nitrile seal but this doesn't have lugs which are required for butterfly valves metal to metal seals arnt allowed either
 
Status
Not open for further replies.

Reply to butterfly valves in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
178
I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
234
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
112
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Replies
1
Views
130
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
182
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock