Having problems with a designer column radiator that I bought. To cut a story short, it gets hot, all columns are hot to touch, tip, middle and bottom but it doesn't heat the room at all. After about an hour all other rooms are hot but the one with the column rad is cold even though it is hot to touch. The btu rating is 4705 at 60 C. Btu calculations for the room average 3500 so should be plenty. Is there any way of measuring the actual btu output? Do new rads go faulty? Anyone with experience on how to approach the company? Initial enquiries have drawn a blank...


Dave from Siberia
 
Can you tell us the exact rad, where its fitted in the room and the room dimensions please.
 
Hi. Thanks for the swift reply. Bilbo Anthracite Double Panel designer radiator with Mirror 1800x381. It's fitted to an outside South facing wall. image.jpg. This is one btu calculation with the dimensions.

Dave
 
This is a Common issue with so called designer radiators IMO and experience. If you look at the design of a modern double panel radiator the actual area that radiates heat is 4 times larger than the radiator area. It also has heat dispersal fins to aid radiation. Panel rads are fitted close to the ground so that the area of convection is greater. Black is not a good radiant colour, white is the best.
You may also have some insulation issues in that one room.

It is possible that the BTU rating of that particular rad has been overstated. Another check would be to take the surface temp of the radiator to see if it is getting hot enough, and then maybe try and balance the heating system. Plenty of advice on how to do that on the web.

But my suspicion is you will never get that rad to heat the room.
 
Last edited by a moderator:
This is a Common issue with so called designer radiators IMO and experience. If you look at the design of a modern double panel radiator the actual area that radiates heat is 4 times larger than the radiator area. It also has heat dispersal fins to aid radiation. Panel rads are fitted close to the ground so that the area of convection is greater. Black is not a good radiant colour, white is the best.
You may also have some insulation issues in that one room.

It is possible that the BTU rating of that particular rad has been overstated. Another check would be to take the surface temp of the radiator to see if it is getting hot enough, and then maybe try and balance the heating system. Plenty of advice on how to do that on the web.

But my suspicion is you will never get that rad to heat the room.

Thanks for the reply Radioman. This seems to be the general consensus regarding designer rads. I am not happy that it is described as offering "exceptional heat output...". Will try balancing the system as you advise and will let you know the outcome.
Thanks for replying, Dave
 
A few quick points.
1st Are you sure you've got the wall type correct ?
2nd Have you checked the delta T on the rad ?
3rd I think your on line heat loss device /calc is wrong. It should be higher
 
Thanks for the reply. Yes, the wall type is correct. Also the area of the room I have overestimated by a quarter due to its shape. I tried four different sites for btu calculations and none came anywhere near the rads btu figure. The Delta T? Don't know what that is but I'll read up on it thanks

Dave
 
Last edited:
Thanks for the reply. Yes, the wall type is correct. Also the area of the room I have overestimated by a quarter due to its shape. I tried four different sites for btu calculations and none came anywhere near the rads btu figure. The Delta T? Don't know what that is but I'll read up on it thanks

Dave
Basically it is the difference between the room temp and surface of rad temp.
Have a look at what the rad manufacturers give as delta T when they give the output. The delta is symbolised with a triangle as you probably know. So it will be a triangle with a number. The number will be temp diff in Centigrade. So for example, Delta T 50, means that if you wanted your bedroom at 18 degrees C, you would need the surface temp of a correctly sized rad at 68 deg mean temp. This is normally taking it that the outside temp will be minus 1 degree Centigrade.

Using a mear calculator and the room size you give I would be looking around 5100 Btu,s /hr Heat requirements
This is possibly a little oversized but it is what I have always used and it will cope better with a bad winter. If you are very exposed, add 10%. It is not an exact science so don't get hung up on exact measurements, there are many other factors that will effect these calculations, such as you over sizing the room.

That requirement given is my own personal way of doing it using the method I have always used and the sizes you gave. Others may disagree, or indeed have different methods and reach different results but they should be similar.

I hope this helps you.
 
Basically it is the difference between the room temp and surface of rad temp.
Have a look at what the rad manufacturers give as delta T when they give the output. The delta is symbolised with a triangle as you probably know. So it will be a triangle with a number. The number will be temp diff in Centigrade. So for example, Delta T 50, means that if you wanted your bedroom at 18 degrees C, you would need the surface temp of a correctly sized rad at 68 deg mean temp. This is normally taking it that the outside temp will be minus 1 degree Centigrade.

Using a mear calculator and the room size you give I would be looking around 5100 Btu,s /hr Heat requirements
This is possibly a little oversized but it is what I have always used and it will cope better with a bad winter. If you are very exposed, add 10%. It is not an exact science so don't get hung up on exact measurements, there are many other factors that will effect these calculations, such as you over sizing the room.

That requirement given is my own personal way of doing it using the method I have always used and the sizes you gave. Others may disagree, or indeed have different methods and reach different results but they should be similar.

I hope this helps you.
Thanks again for the reply. I feel like I'm getting somewhere now. I will email the manufacturer for the Delta number. It was unusual that there were no specs when the boxed rad was delivered, only the fitting measurements.The fitter commented on this.

Dave
 
I always explain to the Customer that these rads aren't as efficient as a regular convector rad!

This comes after having fitted 2 in one house & having to change them lol, they were like hot water bottles on the wall, hot to touch but no heat deflected into room!
 
At the end of the day i'm afraid this comes down to you.
They gave the information you required ie 4705btu @60ºΔT which means 4705btu at a mean water to air temperature of 60º. This is not a viable way of calculating anything as generally the air temp will be 20º+(bedrooms used to be 18º but these days a bedroom is expected to be as warm as a lounge) and the mwt will be anything between 76 (max unless poorly installed) to <50º with a condensing boiler. This means your ΔT is between 30 and 56 and the lower the ΔT the lower the output.
If you contact the manu they will give you correction factors that are applied to the given outputs to give you the outputs at any given ΔT eg at a ΔT of 50 the correction factor may be 0.78 so the 4705 btu drops to 3670btu
Btw dark colours radiate more heat but unfortunately radiators radiate very little. They convect heat. An example of this is hold your hands 6" from your radiator and you won't feel much heat but hold your hands 6" from an open fire and you won't keep them there long.
There is a bit more to the heating game than can be looked up on an internet unless you know exactly what you are looking for.
In the meantime a couple of these will help with with radiation heatloss [DLMURL="http://www.sportsdirect.com/lee-cooper-cooper-winter-beanie-hat-mens-909015?colcode=90901503"]Lee Cooper | Lee Cooper Winter Beanie Hat | Men's Winter Accessories[/DLMURL] ;)
 
Last edited by a moderator:
Totally take your point Tamz about the Internet and would never attempt to do a heating related job myself. Dug the hot water bottle out last night and it burst because the rubber had perished:grin: will call in a heating engineer to give the whole system the once over and see if there is anything that can be tweaked. If nothing can be done will take advice on what to fit in its place and I will go back to the place of purchase to see if some deal can be done.
I appreciate any time you guys have given me, as I say I would never attempt anything like this myself but do like to understand a little about what others do.

I will post the outcome so that others in a similar situation can read it and not take up anyone else's time.

Dave
 
Question:

Do you have a condensing boiler and what temperature is the flow set to?

If we had that information, correction factors could be given and the rated heat output could be made.

The way I read the figures you have been given is:

90C Flow, 70C Return = Mean water temp 80C.
Less room temp 20C

Delta T = 60 C
 
Question:

Do you have a condensing boiler and what temperature is the flow set to?

If we had that information, correction factors could be given and the rated heat output could be made.

The way I read the figures you have been given is:

90C Flow, 70C Return = Mean water temp 80C.
Less room temp 20C

Delta T = 60 C

Hi Oz, I will get those details later when I'm home. Are you saying that if those figures are correct that the radiator should be performing better, even after three hours with the boiler temp set to max, the room is not even warm, just the chill taken off it. I need to decide a. Whether to bite the bullet and replace the radiator with a same design but much higher output.b. Replace it with a more traditional radiator which will involve much more invasive prep work for the pipework or c. Move out...:mad2:

Dave
 
Hi Oz, it's a Saunier Duval Fanned flue combI boiler and the temperature on the display is set to 74 degrees. Is this the info you require?

Dave
 
Hi Oz, it's a Saunier Duval Fanned flue combI boiler and the temperature on the display is set to 74 degrees. Is this the info you require?

Dave

Assuming its a std efficiency boiler, set at 74º, the MWT at the radiator in a perfect world would be will be 69º but in reality it will be a wee bit lower, so lets call it 67ºC
If you want your room to be 21º this means the ΔT will be 46ºC
Multiply the output by the correction factor
4705*0.71 = 3340btu (just under a kw which for easy thinking is like one bar of an old electric fire)

The actual output of the radiator reduces slightly as the room heats up.
 
Jeez, and I thought the television repair trade was complicated! :lol: Am I to deduce from your calculations that it is giving out the equivalent heat of a one bar electric fire? Or really the answer I'm looking for is, is this radiator, given the details that have been provided, capable of heating adequately a room of the dimensions given or have I been sold a dud or has it been under calculated by me because I focused on the BTU figures only?
I really don't want to take up a lot more of your time, you guys have been more than helpful.

Thanks, Dave
 
Since you are probably old enough to remember bars on an electric fire, it needs about 1 1/2.
Since you couldn't run them at a 1/2........2 to heat the room and 1 to keep it ticking over.
You just took their outputs at face value without realising it needed adjusting.
The highest a boiler stat can go in this country is 82

Turning your boiler up to max will help in the meantime
 
Last edited by a moderator:
[emoji33][emoji33][emoji33][emoji33]2 bars of an electric fire on all night! My Nan would have gone purple! Her stack of "Florins" for the meter would have disappeared toot suite! Guess that gives my age away a bit
 
Thanks guys for your input. Just to end on a funny note regarding electric fires. When I was about 13, (1973) I was left on my own in a cold house with only an electric fire for heat. I switched it on left it for a couple of minutes but the bars didn't go red, so I thought it would be clever to gently put my finger on the bar to see if it was warming up while my other hand was on the metal frame!!! Yep, I yelped like a dog and flew across the room jumped up and ran upstairs in shock. That was one of my nine lives gone! :biggrin5: Didn't put me off messing with electrickery and being a TV engineer for the next forty years!

Dave
 
"Good grief, I thought there was someone knocking on the front door but it was the leccy meter goin round ", said radiomans nan.

My nans was on half and you could hardly see a glow, if I turned it up she'd have a blue fit too.
It was a dangerous business touching those toggle switches.
 
"Good grief, I thought there was someone knocking on the front door but it was the leccy meter goin round ", said radiomans nan.

My nans was on half and you could hardly see a glow, if I turned it up she'd have a blue fit too.
It was a dangerous business touching those toggle switches.

This does bring back such happy memories of my Nanna. She also had a pay as you go gas meter, I think it took either a sixpence or a shilling. There was always a small stack by the meter which she used to take from and send me up the shops for 10 Embassy and a sherbet dip.
One thing I never understood was when the meter men came and emptied the meters they always gave some of the coins back. When I asked my mum why, she said " people who stick there noses where they are not wanted get them chopped off".
 
I always explain to the Customer that these rads aren't as efficient as a regular convector rad!

This comes after having fitted 2 in one house & having to change them lol, they were like hot water bottles on the wall, hot to touch but no heat deflected into room!

Hi. I found this to be the case with towel rads too. Probably similar in design and heat output.
 