Bob Hill

Hi all,

I've just started the above ground discharge section of my level 2 NVQ and am confused by soil stacks and branch connections (the text book doesn't give nearly enough info, just two bad diagrammes).

I've tried searching the forums but no luck.

My issue is with branch connections into soil stacks and cross flow.

According to the building regs part H page 8 - The ways to prevent cross flow are:

- Have connections at the same level but coming in at least at right angles to each other when looked at from above.

- Have the connections offset with regards to the height they enter the stack (variable distance based on stack diameter and what the branches serve).

- Create a parallel junction of at least 50mm so that the branch connects outside the no connection zone

My questions are therefore:

Are there other methods?
How does the angle that the pipe enters the stack at affect things?

Thanks in advance.
 
It says somewhere in the regs that junctions should be at 200mm intervals at a minimum.

The steeper the angle, the less likely any backflow.
 
The JTL book is pretty detailed on this. WHPES is right about the 200mm minimum intervals, although I don't remember anything about intervals being variable according to pipe diameter. Not saying you're wrong, but I don't recall seeing it anywhere. Will check the book when I get a chance...
 
Only the methods in the regs are approved.
Iirc there are diagrams within doc h which highlight the approved methods.
As masood states the JTL books are also good for trainees as it gets the point across in an understandable way. Other books can overcomplicate simple issues.
Good luck

Sent from my GT-I9100 using Tapatalk 2
 
Thanks guys.

I have the JTL book, which is usually pretty good but on this occasion it just gives two pictures with no explanation.

Do people recall if it used to be different. I've seen council flats with two branches joining directly opposite but the last part of each branch is made up of two 45% bends.
 
Status
Not open for further replies.

Reply to Confused by soil stack and branch connections in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

The soil pipe from my bathroom passes through the outside wall and into the roofspace above the adjacent single storey kitchen before dropping...
Replies
4
Views
157
Morning all, as always can never find an exact existing thread / discussion where I don't feel like I'm making one too many assumptions. Can I...
Replies
3
Views
1K
Im looking to install a saniflo or similar, with the outlet rising up through a flat roof and into a soil stack above. The problem is, this...
Replies
18
Views
1K
Attached is a ground floor picture of the soil pipe in our home. There was originally a toilet which has now been permanently capped off and you...
Replies
4
Views
1K
Hello. This is my first ever post asking for help. I had a bathroom renovation done early this year which I did myself. I wanted to have a low...
Replies
0
Views
742
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock