Worcester 24i RSF (CDI style)
Tenant reported the hot water was overly hot. Arrived, tested burner pressures, 11.5mb max, 3.4mb min, should be 13.6 and 1 respectively but seeing as the water is too hot, didn't touch and potentially make worse. Check hot water sensor/thermistor. Phoned technical whilst there to confirm resistance of thermistor, tech guy says its out of range, ideal. Ordered a new temp sensor.
Re-visit, fit sensor, check water, still the same. Phone tech, ask for the voltage for the modureg unit on gas valve. Tech guy, obviously reading off the chart says voltages are wrong and his fault chart says PCB. OK, wasn't overly convinced but authorised to change so ordered up.
Re-visit, fit PCB, fire up... the same. Annoyed now, re-test burner pressures, same as before. Decide to adjust B.P, max up to 13.6mb fine, minimum oops to low, down to 0mb.... hang on, boiler is still lit?
Scratch head.
scratch head.
Get other guage from van, 0mb. Boiler is still firing well, not just a tickle on the burner.
Notice a pilot adjustment on gas valve, pretty sure the RSF range were all auto ignition, phone technical, this gas valve was never fitted to this boiler.
Anyway to cut a long story short, the boiler was ID'd and a new boiler is going in, but can anyone explain how the gas is bypassing the test nipple? I'm stumped, can only presume its an internal fault to the gas valve, but has anyone come across it before?
Tenant reported the hot water was overly hot. Arrived, tested burner pressures, 11.5mb max, 3.4mb min, should be 13.6 and 1 respectively but seeing as the water is too hot, didn't touch and potentially make worse. Check hot water sensor/thermistor. Phoned technical whilst there to confirm resistance of thermistor, tech guy says its out of range, ideal. Ordered a new temp sensor.
Re-visit, fit sensor, check water, still the same. Phone tech, ask for the voltage for the modureg unit on gas valve. Tech guy, obviously reading off the chart says voltages are wrong and his fault chart says PCB. OK, wasn't overly convinced but authorised to change so ordered up.
Re-visit, fit PCB, fire up... the same. Annoyed now, re-test burner pressures, same as before. Decide to adjust B.P, max up to 13.6mb fine, minimum oops to low, down to 0mb.... hang on, boiler is still lit?
Scratch head.
scratch head.
Get other guage from van, 0mb. Boiler is still firing well, not just a tickle on the burner.
Notice a pilot adjustment on gas valve, pretty sure the RSF range were all auto ignition, phone technical, this gas valve was never fitted to this boiler.
Anyway to cut a long story short, the boiler was ID'd and a new boiler is going in, but can anyone explain how the gas is bypassing the test nipple? I'm stumped, can only presume its an internal fault to the gas valve, but has anyone come across it before?