Discuss Firebird Riello Motor Hot in the Oil and Solid Fuel Forum area at PlumbersForums.net

Motors will obviously be quite hot when running at steady state, could not tell you what sort of temperatures are normal though, lots of variables can effect that.
Running for 10-15 minutes though at a time suggests possibly a fuel issue. I think the temperature of the motor is irrelevant to your lockout problem now.
See if you can get a shorter video of flame failure and retry cycle, that would help.
Thanks again, SJB060685.
To his credit, the engineer did visit again yesterday, 8:30pm! I was working, but my wife says he checked connections etc., and is himself quite
frustrated by this problem. He's still trying to contact particular people at Firebird and/or Riello. Btw, once in lockout, we get an on/off flashing red
from the control box ... 'Lockout for false flame or parasite flame signal'. This will only reset after several minutes of cooling down. Wondering if I should
buy a replacement capacitor (long-shot) just to see if it helps! I've checked btw that the old and new capacitors have exactly the same ratings: 4,5.
20211004_225151.jpg
 
False flame signal or parasitic light as they call it in the manuals could be caused be either faulty photocell or the control box itself. It could also it's actually detecting false light on prepurge cycle.
Based on the above you've just now said i don't think the capacitor is contributing to the fault but as I said in my original response a faulty capacitor can cause the motor to run hotter. Basically if a capacitor is weak or a larger microfarad cap is used you will get an Imbalance between the pole magnetic fields within the stator, this causes the motor to stutter, or even stall completely. If the motor is stuttering it will draw more current than in usual steady state operation and as a result runs hotter. There's two ways to test a capacitor but the one that would tell us just what the capacitance rating of the cap is requires a multimeter that can read capacitance. If you were to get a reading of 70% or less than the original 4.5uF then capacitor should be replaced. One way of getting an idea if the capacitor is struggling is when there's a demand at the burner, if the motor spins instantly it's ok but if there's a slight lag that is an indication it needs replacing.
 
Thanks again, SJB060685.
To his credit, the engineer did visit again yesterday, 8:30pm! I was working, but my wife says he checked connections etc., and is himself quite
frustrated by this problem. He's still trying to contact particular people at Firebird and/or Riello. Btw, once in lockout, we get an on/off flashing red
from the control box ... 'Lockout for false flame or parasite flame signal'. This will only reset after several minutes of cooling down. Wondering if I should
buy a replacement capacitor (long-shot) just to see if it helps! I've checked btw that the old and new capacitors have exactly the same ratings: 4,5.View attachment 64233
 
See as soon as you press the lockout reset button and you hear it click inside the control box that motor should spin. As I mentioned above and as the video you just shared demonstrates there is a lag/delay. This could be the capacitor but it could also be the control box, sticking pump, fan, bearings. If the pump is new that shouldn't have any tight spots but it's not uncommon for parts to be faulty off the shelf. Also a tip for you and your engineer is everytime a new pump is installed replace the capacitor at the same time. The motor is new as well, so again the bearings should be fine and if the fan was catching you would almost certainly hear it rubbing against the fan housing.

As it stands I think possibly a control box giving you a couple different problems, or one problem in the false light situation and possibly the capacitor. The photocell could also cause parasitic light failures.
I appreciate your engineer has gone above and beyond for you and I'm not slating him in anyway, he's obviously tried and frustrated he's become stuck but control boxes, pumps, cells, capacitors etc should all be van stock.
Again you need a way of reading the capacitance value of a capacitor to determine its rating in uF, without it you just be guessing.
 
Managed to upload this short video ... 22 secs.
I like the idea of a faulty photocell, as this might explain (I think) why a 'cooling down' period is required after those 10 - 15 minutes of burn time, before each lockout. We have to bear in mind though that the whole system was running fine until that initial lockout some 2 weeks ago.
The engineer reckoned the kerosene pump was too stiff, and so replaced it. I still have it as a souvenir, and sure enough, you can't turn it with the fingers.
Perhaps though, that wasn't related to the real reason for that initial lockout?
Also, wondering if the fire cut-out device (on the in-coming oil-line) is kicking in and depriving the boiler of oil?
Cheers.
 
If you can you can freely spin the old pump by hand without any tight spots then I highly doubt that needed changing.
If the fire valve was cutting in to stem oil flow then it would need to be manually reset. You haven't mentioned needing to do this, therefore that is not the problem.
Unfortunately anything can develop a problem at any time, even boilers kept in immaculate condition and serviced regularly will develop problems and unfortunately for you photocells and control boxes are very common faults on Riello burners.
 
See as soon as you press the lockout reset button and you hear it click inside the control box that motor should spin. As I mentioned above and as the video you just shared demonstrates there is a lag/delay. This could be the capacitor but it could also be the control box, sticking pump, fan, bearings. If the pump is new that shouldn't have any tight spots but it's not uncommon for parts to be faulty off the shelf. Also a tip for you and your engineer is everytime a new pump is installed replace the capacitor at the same time. The motor is new as well, so again the bearings should be fine and if the fan was catching you would almost certainly hear it rubbing against the fan housing.

As it stands I think possibly a control box giving you a couple different problems, or one problem in the false light situation and possibly the capacitor. The photocell could also cause parasitic light failures.
I appreciate your engineer has gone above and beyond for you and I'm not slating him in anyway, he's obviously tried and frustrated he's become stuck but control boxes, pumps, cells, capacitors etc should all be van stock.
Again you need a way of reading the capacitance value of a capacitor to determine its rating in uF, without it you just be guessing.
Thanks again, SJB060685.
The engineer will hopefully return on Thurs evening (when we're not at work), and I'm tempted to message him in advance to request a change of
both Control Box and Photocell . . . one at a time of course. Part-Changing exercise I know, but the whole system is too new for it to be anything more
than a simple, albeit annoying, little fault. Thanks for watching that video; your expertise is really very much appreciated.
Cheers.
Alan.
 
If you can you can freely spin the old pump by hand without any tight spots then I highly doubt that needed changing.
If the fire valve was cutting in to stem oil flow then it would need to be manually reset. You haven't mentioned needing to do this, therefore that is not the problem.
Unfortunately anything can develop a problem at any time, even boilers kept in immaculate condition and serviced regularly will develop problems and unfortunately for you photocells and control boxes are very common faults on Riello burners.
Brilliant advice. Thank you!!!
 
Thanks again, SJB060685.
The engineer will hopefully return on Thurs evening (when we're not at work), and I'm tempted to message him in advance to request a change of
both Control Box and Photocell . . . one at a time of course. Part-Changing exercise I know, but the whole system is too new for it to be anything more
than a simple, albeit annoying, little fault. Thanks for watching that video; your expertise is really very much appreciated.
Cheers.
Alan.

I'm happy to help, obviously there's only so much that I can do through typing a message over a phone though. Oil burners is my official trade but I'm just as passionate about heating systems and electricity as well. I don't know everything, there's still a long way to go but studying is the only way someone will get there.
 
I'm happy to help, obviously there's only so much that I can do through typing a message over a phone though. Oil burners is my official trade but I'm just as passionate about heating systems and electricity as well. I don't know everything, there's still a long way to go but studying is the only way someone will get there.
Hello again, SJB060685.
Photocell !!! That was the problem. Once you'd suggested the Control Box and Photocell as being common problems on the Riello units, I sent a text to my engineer.
He was doing his own research too, and enthusiastically returned two days ago, quickly changing the photocell. That did the trick! However, not before he'd tried a couple
of photocells . . . one being analogue and the other being digital. I'm not sure as to which one he ended up fitting, but I'll find out hopefully.
Thanks again, SJB060685. Hopefully this thread will help others too.
Best wishes.
Alan.
 

Reply to Firebird Riello Motor Hot in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

S
Having a few issues with my combi boiler, its 14 years old now and due to be replaced as we are building extension, but need to get another 10...
Replies
3
Views
950
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
S
Worcester Danesmoor 20/25, about 18 years old. B11 burner. We came home a few days ago to find our boiler in lockout, and not wanting to restart...
Replies
1
Views
2K
P
Hi. I have a hot water high pressure problem that my heating engineer (and other engineers that he has spoken to) cannot fix. I’m hoping someone...
Replies
4
Views
1K
I currently have a Vaillant ecoTEC Plus 438 system boiler which is 13 years old. I have been having problems with the boiler which potentially...
Replies
6
Views
708

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock