I can't find anything in the viper book about this.

Minimum distance from flue to boundary of next house is 600mm..

What if that wall had 2 air bricks and a vent??

Actual distance is 1.3m.

Gonna replace the boiler but need to know if I need a plume kit. Will be fitting a Vaillant ecotec Plus 624.

Flue on left vents on right in pic.

90d8a7474bf2c08813cf7b612ecb2029.jpg
 
The only thing I can find in the regs is 2000mm from an opening in adjacent building.
 
K=1200mm minimum distance from another flue terminal so just about OK but below is from Part J Building Reg.

Outlets from flues
3.23 Outlets from flues should be so situated externally as to allow the dispersal of products of combustion and, if a balanced flue, the intake of air. A way of meeting this requirement would be to locate flue outlets as shown in Diagram 34 and Diagram 35.
Note: The plume of wet flue products from condensing boilers, positioned in accordance with the safety distances set out in Diagram 34, can sometimes be considered a nuisance for neighbouring properties. Whilst this nuisance is not considered to be within the scope of building regulations, such installations could be considered as a ‘Statutory Nuisance’ as set out in the Environmental Protection Act. As such installers may wish to adopt the guidance in Chapter 6 of the Guide to Condensing Boiler Installation Assessment Procedure for Dwellings
Care may also need to be taken to locate flue outlets away from parts of the building that may be damaged by frequent wetting.


I would suggest a plume kit Jay, discharging products of combustion over the building boundary into someone else property is never a good idea & if wanted to get snotty they could make you alter it.

http://webarchive.nationalarchives....l.gov.uk/uploads/br/br_pdf_ptl_condboiler.pdf

Section 6 suggests 2.5 Meters to boundary !!!
 
Last edited:
K=1200mm minimum distance from another flue terminal so just about OK but below is from Part J Building Reg.

Outlets from flues
3.23 Outlets from flues should be so situated externally as to allow the dispersal of products of combustion and, if a balanced flue, the intake of air. A way of meeting this requirement would be to locate flue outlets as shown in Diagram 34 and Diagram 35.
Note: The plume of wet flue products from condensing boilers, positioned in accordance with the safety distances set out in Diagram 34, can sometimes be considered a nuisance for neighbouring properties. Whilst this nuisance is not considered to be within the scope of building regulations, such installations could be considered as a ‘Statutory Nuisance’ as set out in the Environmental Protection Act. As such installers may wish to adopt the guidance in Chapter 6 of the Guide to Condensing Boiler Installation Assessment Procedure for Dwellings
Care may also need to be taken to locate flue outlets away from parts of the building that may be damaged by frequent wetting.


I would suggest a plume kit Jay, discharging products of combustion over the building boundary into someone else property is never a good idea & if wanted to get snotty they could make you alter it.

http://webarchive.nationalarchives....l.gov.uk/uploads/br/br_pdf_ptl_condboiler.pdf

Section 6 suggests 2.5 Meters to boundary !!!

Thing is there's a light to the right, a window above and a roof to the left. I was thing of putting a deflector kit and kicking it to the right and up 45 degrees.l so the plume goes down the alley..?
 
Status
Not open for further replies.

Reply to Flues and vents in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
294
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
272
PSxxxxxx
P
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
271
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
305
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock