Horizontal and vertical flues

Existing installations no clips on extensions definitely AR? Or defect? Bit of a grey area, also self tapper screws? Ar or defect? If flue has neither but is solid would you leave on?
 
See GS(IU)R 27 and 28 - it is not a grey area, the regulations are very prescriptive.

If there is any leakage of Products of Combustion (POC) from the flue joints, appliance or condensate air break - it is ID

If there is no leakage of POC:

Insecure or inadequately supported flue it is AR

Incorrect jointing methods of the flue, screws missing or inappropriate lubricant used on push fittings it is AR
 
Last edited:
See GS(IU)R 27 and 28 - it is not a grey area, the regulations are very prescriptive.

If there is any leakage of Products of Combustion (POC) from the flue joints, appliance or condensate air break - it is ID

If there is no leakage of POC:

Insecure or inadequately supported flue it is AR

Incorrect jointing methods of the flue, screws missing or inappropriate lubricant used on push fittings it is AR
So if you had a terminal not 300mm from an openable window but less, but no POC was entering the property, would you class as defect or ID? Im hearing lots of opinions recently
 
So two parts of the GS(IU)R to consider:

Non- Compliant Terminal position is covered by regulation 27 would be AR, provided always that products of combustion (poc) are not entering the building.

The process for the Assessment of the Risks for poc to re-enter a building are set out in Gas Safe Technical Bulletin TB007.

So, the answer to your point for the terminal you described is AR. However, you would need to be satisfied and to be able to demonstrate that the requirements of TB007 had been taken into account, in making your decision, in the event of any subsequent issues.

Obviously if poc are re-entering the building, then it is ID.
 
Last edited:
So if you had a terminal not 300mm from an openable window but less, but no POC was entering the property, would you class as defect or ID? Im hearing lots of opinions recently

Ar I would class it as
 
So two parts of the GS(IU)R to consider:

Non- Compliant Terminal position is covered by regulation 27 would be AR, provided always that products of combustion (poc) are not entering the building.

The process for the Assessment of the Risks for poc to re-enter a building are set out in Gas Safe Technical Bulletin TB007.

So, the answer to your point for the terminal you described is AR. However, you would need to be satisfied and to be able to demonstrate that the requirements of TB007 had been taken into account, in making your decision, in the event of any subsequent issues.

Obviously if poc are re-entering the building, then it is ID.
Thanks for clearing that up bud
 

Reply to Flues (AR and ID) would like to lnow what fellow gas engineers think of this grey area in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
501
Show us your fanciest radiators you've installed! We would love to see them! I love this Milano vertical radiator in the kitchen space. What do you think?
Replies
4
Views
230
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
248
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
218
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
213
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock