Can anyone help me identify which tap/connection it is to top up the system as the level has dropped quite a way below the red marker for the cold fill pressure on the gauge? Boiler was installed approx. 2014. I've looked in the manual & online but can't find anything. Many thanks
 

Attachments

  • BoilerB.jpg
    BoilerB.jpg
    393 KB · Views: 22
  • BoilerA.jpg
    BoilerA.jpg
    405.8 KB · Views: 17
need more pics can not see any thing there.

Off the balanced cold

Op do you see the red band black body ariston valve there’s a silver flexi pipe off that there will be a valve on that eg behind the pipe in the right photo

Pressure wants to be around 1 bar which by the looks it is (cold)
 

Attachments

  • IMG_8422.jpeg
    IMG_8422.jpeg
    215.9 KB · Views: 14
need more pics can not see any thing there.
Sorry! Doesn't help that I have no idea what I'm looking at...

Just taking these photo's now & I've noticed one of the blue taps at the bottom, last photo BoilerH, does actually say 'cold in', but i've just turned this & nothing has happened. The heating is off at the moment, does it need to be on & try that tap?

Thanks again for any replies
 

Attachments

  • BoilerH.jpg
    BoilerH.jpg
    366.6 KB · Views: 11
  • BoilerG.jpg
    BoilerG.jpg
    461.9 KB · Views: 12
  • BoilerF.jpg
    BoilerF.jpg
    343.1 KB · Views: 13
  • BoilerE.jpg
    BoilerE.jpg
    352.5 KB · Views: 11
  • BoilerD.jpg
    BoilerD.jpg
    333.7 KB · Views: 13
  • BoilerC.jpg
    BoilerC.jpg
    313.3 KB · Views: 14
just added more, do they help? no idea what your comment means, sorry.

Edited my reply do you have a problem/ something wrong as it should be working ?
 
Edited my reply do you have a problem/ something wrong as it should be working ?
Thanks, it is working, but the user manual I have states that system top up is required if the black marker on the gauge falls below the red cold fill pressure marker? Last year the black marker was only just under the red, it's dropped lower now, so i'm asking how to top up?
 

Reply to GAH Electrastream boiler, low pressure level, how to top up system? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
270
PSxxxxxx
P
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
207
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
205
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
426
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock