Discuss Gas Inspector (and me) got it wrong!!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
P

princegoose

I mention in another post that I had to AR a Boiler while doing a landlords gas safety check in front of the GS inspector. While doing the visual checks he told me to look at the flue and asked me to tell him what was wrong. Of course I didnt get it straight away but guessed it was too close to the door (less that 300mm).

The landlord was very unhappy and was trying to convince me id got it wrong.

So to prove myself right I went back and measured the distance of the flue from the door.

it was bang on 300mm. egg on my face.

there is a brick gate post too close to it which Id class as an internal corner, but that can be knocked down easily, so will get to do a cp-12 pass next week once its done.

would the 'too close to internal corner' AR the boiler as well?

Should I tell the inspector? tbh I didnt measure the flue distance while he was there as I thought it was less than 300mm too.
 
Last edited by a moderator:
When you AR'd the boiler ... was it simply because it was within in 300mm? Or did you have other factors such as poor FGA readings, reports fumes from the tenant or evidence of POCs entering the building?
 
If its an existing install and all combustion check are ok and it is not too close to external/internal corner (bit of a judgement call) then at worst it NCS. Only if its a recent install would it be AR.
 
Last edited:
nope, just distance of flue from door. fga was 0.0003%, well within. tenant said thered never been a problem.

why?
 
If its an existing install and all combustion check are ok and it is not too close to external corner (bit of a judgement call) then at worst it NCS. Only if its a recent install would it be AR.

really??? has it changed recently? because on my life the GS inspector said it its AR.
 
I would class this as NCS myself and note it on my cert. I often come across borderline flue to door openings/window openings and if I AR each one I'd be forever filling out forms and would have tons of unhappy landlords.

I was always led to believe that two or more faults on flueing and ventilation was then classed as AR or ID depending on the situation.
 
it hasnt changed as others have said, but a flue 299mm from a brick cant be AR, (i assume you did measure from the edge of the flue and not the edge of the air intake, ) have seen some do that, it wwill only be AR if it is too close and has scorched a combustible surface, i appreciate the dimension must be adhered to but common sense has to prevail, someone clever decided it needs to be 300mm but the safety factor will have been built in to this dimension so just under 300 to a brick must only be NCS surely
 
it hasnt changed as others have said, but a flue 299mm from a brick cant be AR, (i assume you did measure from the edge of the flue and not the edge of the air intake, ) have seen some do that, it wwill only be AR if it is too close and has scorched a combustible surface, i appreciate the dimension must be adhered to but common sense has to prevail, someone clever decided it needs to be 300mm but the safety factor will have been built in to this dimension so just under 300 to a brick must only be NCS surely

it was 300mm to the opening of the door, but less than 20mm to the brick post, which potruded less than a soil stack (half brick), but i figured it would more likely be classed as a corner, as everyone wants to cover their back.....
 
it hasnt changed as others have said, but a flue 299mm from a brick cant be AR, (i assume you did measure from the edge of the flue and not the edge of the air intake, ) have seen some do that, it wwill only be AR if it is too close and has scorched a combustible surface, i appreciate the dimension must be adhered to but common sense has to prevail, someone clever decided it needs to be 300mm but the safety factor will have been built in to this dimension so just under 300 to a brick must only be NCS surely

I was taught it has to be from air intake not flue. Is this a case of MI in some cases?
 
May be the inspector made a engineering Judgement call.

Refer to industry unsafe sits proceedure, section 8 page 38.
8.3: Covered passage way or carport or the like AR.
8.4: Close proximity to doors and windows. Carry out an assessment using ECGA to BS7967, If it fails ID.
8.5: To close to boundaries ect NCS.

Measurement must be taken from the outer edge of the flue terminal. On a concentric flue this is from the edge of the air intake at the terminal. Also refer to BS5440 Part 1 Appedices C table C2. Input of boiler relative to distance from opening. Manufacturer instructions have the over riding requirement though.
 
I would class this as NCS myself and note it on my cert. I often come across borderline flue to door openings/window openings and if I AR each one I'd be forever filling out forms and would have tons of unhappy landlords.

I was always led to believe that two or more faults on flueing and ventilation was then classed as AR or ID depending on the situation.
It is at individuals discretion/interpretation wither multiple NCS's should warrant being elevated to an 'AR' classification. A couple of minor flue/ventilation NCS's does not automatically mean 'AR'.

it was 300mm to the opening of the door, but less than 20mm to the brick post, which potruded less than a soil stack (half brick), but i figured it would more likely be classed as a corner, as everyone wants to cover their back.....
Being overcautious is almost as bad as not being thorough enough. You should be making a call based on facts and regulations. Unfortunately, most of the regs are not black & white. You have to interpret them to the best of your ability and make your call. If in doubt seek advice. Back up your findings on paperwork.
it hasnt changed as others have said, but a flue 299mm from a brick cant be AR, (i assume you did measure from the edge of the flue and not the edge of the air intake, ) have seen some do that, it wwill only be AR if it is too close and has scorched a combustible surface, i appreciate the dimension must be adhered to but common sense has to prevail, someone clever decided it needs to be 300mm but the safety factor will have been built in to this dimension so just under 300 to a brick must only be NCS surely
A concentric flue is a unit and any measurements should be taken to the outside of the flue in my opinion.
 
Also, if customer complains of fumes/plumbing etc etc coming into property it would effect NCS/AR outcome... Due to the close proximity to the door/window
 
Strange that but i was taught at collage last year that 2 NCS s on fluing and ventilation should be upgraded to AR.
 
Strange that but i was taught at collage last year that 2 NCS s on fluing and ventilation should be upgraded to AR.
Think about it!
So, flue 1900mm high with no terminal guard and flue 290mm from window instead of MI's stated 300mm automatically means 'AR'. Even though all safety checks pass. You were taught to be overcautious.

Unsafe sits maps it out for ye. Only if you decide the multiple NCS's are serious enough would it be upgraded to 'AR'.
 
Status
Not open for further replies.

Reply to Gas Inspector (and me) got it wrong!!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock