Hi guys not sure anyone has encountered this before but I have a job where the inside wall has been getting a little damp, there was a step up to the door that I think wasn't helping due to dpc but that was removed to take a closer look and it revealed 2 waste water pipes going into the patio floor, I went and had a look to see if leaking and couldn't directly see anything leaking but when I inspected the termination of the waste pipes they are just dangling into a gully that has been patio'd over? I'm no damp expert but could this be causing the problem, I imagine it is at least something to do with this so I am going to reroute the pipework into the stack that's nearby, I think it'll just about make it but it's not ideal at all. I've attached a photo so you better understand what I mean. I will be pressure testing the pipework just incase there is a leak under the tiled floor but I think they are 3m lengths. Thoughts? Thanks. Chester
 

Attachments

  • IMG-20230921-WA0008.jpg
    IMG-20230921-WA0008.jpg
    724.9 KB · Views: 17
Update, pipe on right is compromised, failed pressure test, inspection with camera can see a joint directly where the tiles begin to sound 'hollow', upsized left pipe and temp fix running everything through the 1¼ under basin as it's under a tiled floor so not an easy fix.
 

Reply to Gully patio'd over in use in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

60's ranch, with single bathroom. Tile over concrete slab. Toilet is about a foot from exterior brick wall. Vent pipe is in interior wall behind...
Replies
1
Views
214
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
259
Some advice please about a really worrying problem. I live in a terraced 2 bed room house. 10 days ago the gas combi boiler stopped heating the...
Replies
3
Views
535
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Replies
1
Views
334
Hi, we've just had someone round to fit lino in our toilet. He ripped up the old lino only to reveal a large wet patch around the toilet (see...
Replies
11
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock