Feed/expansion pipe/tank? Having looked at the layout of these (not really looked since college days 17 years ago 😳), I’m possibly understanding the problem.

And if sealed system and prv after pump like it normally is
 
Certainly, all (admittedly only a dozen or so) the OV oil fired systems that I've come across have PRVs installed, most are on the boiler casing itself, not 100% sure but I think my 16 year old Firebird came with the PRV already fitted.
 
This is from some very old FAS (Irish) training course "Trade of Plumbing" but mentions a BS standard.

Open Vent Pipes and Safety Valves
The open vent pipe of non-ferrous material and minimum diameter of 22mm should be sited
so that it can discharge into the F&E cistern above the overflow level. The pipe should rise
continuously and avoid any horizontal runs. Any heated water which may be discharged from
the boiler must have a clear unobstructed path via the open vent pipe to the F&E cistern.
No valves or components, other than full bore pipe fittings, must therefore be fitted at a point
between the boiler and the discharge point of the system.
In addition to the open vent pipe, a safety valve should be fitted on the boiler or on the flow
pipe as near to the boiler as practicable. The location should enable visual indication if the
valve has lifted, but should not be in a position that could be a hazard to any person or
electrical
components in the event of discharging. Safety valves should conform toB.S. 759
In our previous diagrams we have shown the ideal locations for the cold feed and open vent,
in practice however you may find that they are actually part of the pipework circuit from the
boiler, show in the diagram below.
 
This is from some very old FAS (Irish) training course "Trade of Plumbing" but mentions a BS standard.

Open Vent Pipes and Safety Valves
The open vent pipe of non-ferrous material and minimum diameter of 22mm should be sited
so that it can discharge into the F&E cistern above the overflow level. The pipe should rise
continuously and avoid any horizontal runs. Any heated water which may be discharged from
the boiler must have a clear unobstructed path via the open vent pipe to the F&E cistern.
No valves or components, other than full bore pipe fittings, must therefore be fitted at a point
between the boiler and the discharge point of the system.
In addition to the open vent pipe, a safety valve should be fitted on the boiler or on the flow
pipe as near to the boiler as practicable. The location should enable visual indication if the
valve has lifted, but should not be in a position that could be a hazard to any person or
electrical
components in the event of discharging. Safety valves should conform toB.S. 759
In our previous diagrams we have shown the ideal locations for the cold feed and open vent,
in practice however you may find that they are actually part of the pipework circuit from the
boiler, show in the diagram below.


Says it all, thank you, trouble is plumbing and heating safe working practises for open vented systems are largely forgotten as there are so few of them around now.
 
I must say the gas boiler (installed in 1978) in the house I grew up in had no overheat stat and it did have a safety valve. Not sure the MI's actually called for one, however. Given the lack of overheat device, it does make sense.

I don't see the problem in this case however. IF the boiler is plumbed with an unobstructed primary flow with the cold feed and vent coming off that primary flow, with the pump (and pump valves) AFTER the F&E close-coupling, having an extra set of valves on the return will make no difference whatsoever as the return can already be isolated from the open vent via the pump valves. The important thing is not to obstruct the flow. The heated water will still have 'a clear unobstructed path' to the open vent even if it will struggle to cold feed and vent at the same time, but you'd hope the modern overheat thermostat would have tripped well before this led to damage.

To be fair, I do see where people are coming from in that it seems inherently safer to plumb boilers in the old-school method where the boiler is in the neutral point between the cold feed on the return and the vent on the flow, but this simply wouldn't work with the restrictive waterways and low water contents in a modern boiler.
 
A valve should absolutely NOT be on the flow between the vent and boiler.

I'd accept in my own house, but I'd want the valve on the flow locked open and a safety label of some kind. If nothing else, I would imagine this could cause serious damage to the heat exchanger in the event the system were brought up to temperature and then the valves shut. I think the contraction of water as it cooled might cause significant damage.

Apologies for not noticing what the fuss was about - I hadn't seen there was an isolator on the FLOW as well as on the return.
 
Last edited:
The quote in post#15 puts it well IMO as it states, "should be fitted".
If you are referring to the safety valves, I agree, and it may have been the law back in those days even in England. This is clearly a modern boiler, however. Surely you aren't suggesting that virtually all modern RGIs (even Shaun!) don't know the rules? I suspect no-one is fitting PRVs or other safety valves as a supplement to open vents because boilers now have built in safety features that can deal with no-flow situations quite effectively (even an 8kW Thorn Apollo from the 1980s will shut down in seconds if an airlock develops in the flow pipe), and because (I assume) the current rules have been relaxed to take this into account.

Obviously if the text you quote is for a semi-gravity system, then it makes even more sense as there will be no pump on the gravity circuit and it is therefore perfectly possible to have this circuit without valves and with no need for valves either.

If I'm right in my above (first paragraph) assumption, then the only issue we should be dealing with is the isolator on the flow. Obviously we can always go one better than the legal requirements, but IF today's law doesn't require a safety valve, then I wouldn't even want to suggest it is 'good practice' on a modern installation.
 

Reply to having a dispute with another installer in the USA area at PlumbersForums.net

Similar plumbing topics

I recently installed new hot and cold feeds to a new downstairs cloakroom. After refilling the system the hot taps were all dribbling, spluttering...
Replies
2
Views
549
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open...
Replies
9
Views
1K
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
669
Sorry I have sort of asked this before, tried professionals but not great 1st experience hence DIY attempt attempt again. 2 completely cold...