Hi
Pump is a danfoss ups 15-70. The setting is on 3 which Worcester recommended. There have been some good suggestions made and I will do some experimenting now.
 
I can't find the pump curves for that model but can't see the need for setting 3, I would try it on setting 2 and even setting 1 might be sufficient, you could try it on both these settings to see if it helps, also you might post a link to your pump as there are other settings as well and also details of the diverter valve.
You might also check the cylinder coil and see if it has a (balancing) gate valve installed on the return and see how many turns open.
 
I can't find the pump curves for that model but can't see the need for setting 3, I would try it on setting 2 and even setting 1 might be sufficient, you could try it on both these settings to see if it helps, also you might post a link to your pump as there are other settings as well and also details of the diverter valve.
You might also check the cylinder coil and see if it has a (balancing) gate valve installed on the return and see how many turns open.
Sorry it's a grundfoss 15-70
 
If one isn't too worried about ultimate HW cylinder reheat times etc then reduced flow rate won't impact greatly, the main tool (apart from coil area) is having a very high boiler flow temperature on HW duty, most boilers now with HW priority boost the boiler flow temperature up to 80C. In any case even if the boiler does cycle a bit when cylinder is approaching its SP, a oil fired boiler is well able for it as it spends its whole life continuously cycling for years on end.
 
If one isn't too worried about ultimate HW cylinder reheat times etc then reduced flow rate won't impact greatly, the main tool (apart from coil area) is having a very high boiler flow temperature on HW duty, most boilers now with HW priority boost the boiler flow temperature up to 80C. In any case even if the boiler does cycle a bit when cylinder is approaching its SP, a oil fired boiler is well able for it as it spends its whole life continuously cycling for years on end.

It's an external oil combi, John.
 

Reply to Hot to stop banging when boiler calls for hot water in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
396
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
289
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
444

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock