Boiler has 28mm pipes to indirect cylinder gravity feed. Pipe exit from boiler is hot (boiler stat no5). Hot water cylinder not hot enough, boiler running 24 hours continuously. Problem only started, previously piping hot. Can only think there is a blockage or restriction in pipe work, but seems unusual in large bore copper. Any ideas?
 
Have you drained the system down ?

Header tank 1/3 full of water ?
 
Things that need checked are, -
Is there a few inches water in expansion and feed tank?
Is there water at top connection to coil?
Is there a blockage in the feed pipe?
 
As B4 small tank in loft is empty and water level in pipes is to low to let it gravitate
 
The older ballvalves that have brass pistons inside them will tend to seize up easily on heating tanks, as the valve rarely needs to replenish water
 
The older ballvalves that have brass pistons inside them will tend to seize up easily on heating tanks, as the valve rarely needs to replenish water
I agree entirely, whats better to fit is a modern foreign valve that will fail and never shut off after a couple of years, that way it will need replacing again lol
 
Check emitters are all okay might need a tweek of a bleed after topping up the f&e.
 
Status
Not open for further replies.

Reply to Indirect cylinder heating problems in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
199
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
149
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
229
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
362