Discuss Is my Navien boiler behaving as expected? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Messages
12
Hi

Can you help me determine if my new Navien lcb700 lsx is working as expected?

I got the Navien oil boiler installed to replaced an old firebird boiler. The new boiler is a condensing oil boiler and I’m not sure if this is working as expected. I’ve a 300 L water cylinder and after one hour of heating the water temperature reaches 40-45C. The cylinder is less than a year old and the thermostat is working well.

When the heat demand is on, the boiler themostat is set to 60C. The burner starts and the boiler lcd panel reaches 60C. The burner will stop and the pump continues to run. When the temperature at the boiler drops to 40C, then the boiler will burn again to 60C. The cycle continues and the 60C to 40C drop takes about 20 minutes.

My question for anyone….is this normal?

Thanks
 
Unvented cylinder?
 
That’s great do you know the size of the boiler kw ?
 
As the coil on the cylinder is 22kw yes you will have some cycling also with the cylinder temp increasing this will also increase cycling/ time before it fires the boiler again
 
As the coil on the cylinder is 22kw yes you will have some cycling also with the cylinder temp increasing this will also increase cycling/ time before it fires the boiler again
Hi
Am I incorrect to expect the boiler to continue to fire until the water in the cylinder has reached the thermostat set temperature?
 
Hi
Am I incorrect to expect the boiler to continue to fire until the water in the cylinder has reached the thermostat set temperature?

Yes or until the boiler is upto temp then it will wait until the temp drops below its threshold then refire and repeat
 
It will be around an hour due to the coil being miss matched
 

Reply to Is my Navien boiler behaving as expected? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, I have an 20yrs heat only potterton 50e boiler with 196x old house - suspended floor - designer radiators, open vent system and hot water...
Replies
1
Views
619
Hi, can anyone tell me which pipes are flow and return please. I removed old leaking 2008 C26 firebird oil boiler in June . We have now...
Replies
2
Views
547
I have a "Firebird Envirogreen Condensing Combi Oil Boiler 26kW" a part has went and I can't find it anywhere, I was at every plumbers merchant...
Replies
2
Views
421
Hi sorry to hijack the thread, but im new to these forums and upon searching for some answers to my below question i come across this thread. I...
Replies
11
Views
2K
I
Dear All, Please kindly advise, i don't know what else to do! Had new boiler Vaillant 424 heat only open vent boiler installed with new flue and...
Replies
53
Views
5K
Deleted member 120897
D