You sure Timmy quick *** packet gives me a drop of 0.8 on 35mm with 14 high bends
 
You can’t have more than 1mb drop from meter to appliance.
to 20k
You have to run the appliance at max, you can’t down rate it.

So I don’t understand what this “loop hole” is?
Loop Hole is, that if you can prove the appliance is working correctly with the correct gas pressures , you may get away with a slightly undersized gas service line.

As stated previously, if you by a 24kW boiler and only require 20kW, commission the appliance to 20 kW and see what your pressure drop is at the appliance.

Is a Gas Inspector going to re calibrate the appliance to maximum and then test the gas line for correct pressures?
 
Loop Hole is, that if you can prove the appliance is working correctly with the correct gas pressures , you may get away with a slightly undersized gas service line.

As stated previously, if you by a 24kW boiler and only require 20kW, commission the appliance to 20 kW and see what your pressure drop is at the appliance.

Is a Gas Inspector going to re calibrate the appliance to maximum and then test the gas line for correct pressures?
This won’t work with a Combi boiler, as you can range rate the heating but the hot water will be the higher output.
 
Loop Hole is, that if you can prove the appliance is working correctly with the correct gas pressures , you may get away with a slightly undersized gas service line.

As stated previously, if you by a 24kW boiler and only require 20kW, commission the appliance to 20 kW and see what your pressure drop is at the appliance.

Is a Gas Inspector going to re calibrate the appliance to maximum and then test the gas line for correct pressures?

I understand that people regularly let a slightly undersized gas pipe pass.

However, to complete commissioning, you need to test the gas pressure on max load, not partial. On a new install I’m installing a test point under the boiler and running other appliances. I’m not letting an undersized gas pipe slide.

However, I’d size the pipe and new boiler demand and know if it needs an upgrade when quoting work (and include the gas upgrade).

Loop Hole is, that if you can prove the appliance is working correctly with the correct gas pressures , you may get away with a slightly undersized gas service line.
Got a source?
 
I understand that people regularly let a slightly undersized gas pipe pass.

However, to complete commissioning, you need to test the gas pressure on max load, not partial. On a new install I’m installing a test point under the boiler and running other appliances. I’m not letting an undersized gas pipe slide.

However, I’d size the pipe and new boiler demand and know if it needs an upgrade when quoting work (and include the gas upgrade).


Got a source?
In new installs, I generally oversize the gas supply pipe.

In existing houses or premises, where the gas supply pipe is borderline to the requirements, things can be done to alleviate the installation of a new gas line.

If the appliance works correctly with a slightly undersized gas supply and you can prove the appliance is working correctly, then there isn't an issue or a necessity to replace the gas line.
We have inspections from auditors on some jobs. At times they will question whether or not the gas supply pipe is the required size.
Operate the appliances and test the inlet gas pressures and if they prove to be adequate - end of story.

I have at times reduced the output of heating only boilers to get the gas supply over the line.
Unless the customer is going to add extra panels or add other gas appliances, then the existing gas supply is adequate.

But that will be up to the person doing the works, whether it me me or someone else
 

Reply to Length of gas pipe from meter to boiler in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a...
Replies
9
Views
774
British Gas servicing the above boiler ramped up the boiler to maximum in the installer menu to do flue gas analysis. They also measured the...
Replies
4
Views
591
Hi guys, first post here So I have been boxing in a number of heating pipes that are throughout my garage since the boiler was located there by...
Replies
1
Views
240
I had a boiler check today all went well, and then he went to check on the gas meter which is in my larder in the kitchen high up on the wall...
Replies
1
Views
683
Hi folks, i've just moved into a property last month and begun to take note of things that may need attention. One of which is the feed to a...
Replies
8
Views
748

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock