Hi went to a Main 24 he today (very much a B rated baxi combi HE)

Boiler works fine 50% of the time. There is a fault on CH & DHW mode which is as follows;

Pump runs, primary flow swith operates, fan runs at full speed but there is no atempt at igniton, then flame failure light comes on, will not reset, you have to turn selector swith on/off a couple of times. or;
When the boiler is fired up in either CH or DHW mode the flame will cut out then straight away fire up again and carry on working.
I have had this probem with the baxi 105he and it was the pcb, i keep a selection of pcbs in the van so tried it on this and it hasnt sorted it.
Im thinking check min burner pressure, air pressure switch (unlikey as it does fire up most of the time) flame sensing electrode.

Any iders?? Anybody come across this probem before??

Will be going back to carryout more checks so will update
Cheers!!
 
Try that air pressure switch. Had it a few times right on the edge of its pressure setting (tiny hole in diaphragm) just creeps off
 
I see what you mean, just enough for the boiler to cut out but not enough for it to not work at all.
I'll update and cheers for the reply!
 
weve had 3 new pcb's on these boilers a few times now, try another.
 
could be airswitch had a few go on the main,pcb tends to give the same fault but they are not weak boards
 
Went back and replaced the air pressure switch- Sorted it!

I noted in the manufactures instructions it says to take the fan out first in order to get to the air pressure switch (HE model) I just loosend off the side panel and got my hands in there, a lot quicker than taking the fan out!!

Good diagnosis guys, and thanks for the replys!
 
pls help. my baxi 24 he burner fails. cannot get it to start up. i am not a plumber unfortunately but would like to see if i can try to rectify the prob with your help
 
pls help. my baxi 24 he burner fails. cannot get it to start up. i am not a plumber unfortunately but would like to see if i can try to rectify the prob with your help

check your condensate pipes not frozen if its a he model
 
Status
Not open for further replies.

Reply to Main 24HE flame failure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
215
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
439
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock