B

Barry Clark

hi. I removed actuator from motorised valve. Spindle at 12 noon so valve should be closed. However hot is flowing through the valve. I can manually turn the spindle about 20 degrees. Is it possible the gland inside is not turning even though spindle is? Many thanks.
 
hi. I removed actuator from motorised valve. Spindle at 12 noon so valve should be closed. However hot is flowing through the valve. I can manually turn the spindle about 20 degrees. Is it possible the gland inside is not turning even though spindle is? Many thanks.

What model valve?

The most common ones IME are Honeywell and the ones I've dismantled have a 'rubber' ball on a crank that is rolled in front of the outlet to close the valve. It's a neat design that works well until it doesn't. You should be able to rotate the shaft with your fingers and 20° is about the normal range. Usual failure mode is the ball gets a dent in it and stops sealing reliably. You can buy a repair kit for about a tenner but I suspect that most people just replace the valve so the customer feels they've got something for their money most of which goes on the time to drain, refill and bleed the system. And then there's the Fernox tax...
 
time for a new valve and body

finding there only lasting 5-10 years (decent valve) could be less
 
What model valve?

The most common ones IME are Honeywell and the ones I've dismantled have a 'rubber' ball on a crank that is rolled in front of the outlet to close the valve. It's a neat design that works well until it doesn't. You should be able to rotate the shaft with your fingers and 20° is about the normal range. Usual failure mode is the ball gets a dent in it and stops sealing reliably. You can buy a repair kit for about a tenner but I suspect that most people just replace the valve so the customer feels they've got something for their money most of which goes on the time to drain, refill and bleed the system. And then there's the Fernox tax...

Thanks for quick response. It appears to be an older Drayton. It only says BGMVSP-2 on label but this Drayton replacement fits it perfectly: http://www.NoLinkingToThis/p/drayton-zone-replacement-valve-actuator/76959?_requestid=445491
I fitted it but still problem, hence my asking if it's possible the valve is damaged internally. The spindle turns but it never shuts off and from what you say it sounds like it's leaking even though closed.
 
drayton have a flapper, you will need to hold it in the shut position (as the flow will open it without the head on)

and tbh heads on there own arnt worth it, its only another £10 or less if your in the trade (about 38 + vat)
 
Ok. But even with the new head on it's still allowing hot water to flow to the CH if there is demand from the HW cylinder, so I guess it's leaking internally even though held closed by the actuator. It's mounted horizontally and is under the floor (had to take up floor tiles and boards to find) and it's at the lowest point of the system. Guess it could be silted up and so not closing fully? Will have to drain and replace with a new unit. Screwfix said they'd refund the head only. Thanks for your help.
 
Ok. But even with the new head on it's still allowing hot water to flow to the CH if there is demand from the HW cylinder, so I guess it's leaking internally even though held closed by the actuator. It's mounted horizontally and is under the floor (had to take up floor tiles and boards to find) and it's at the lowest point of the system. Guess it could be silted up and so not closing fully? Will have to drain and replace with a new unit. Screwfix said they'd refund the head only. Thanks for your help.

yea tbh normally best to change the body as well unless its under 5 years old, and thats good of them
 
Sorry, just had a thought. There is a small black lever on the Drayton actuator head. It seems to be locked in place and I'm not sure how to move it without breaking it? I guess it's meant to be the manual override for filling? There's nothing in the instructions about what it does or how to move it. Sorry, I must sound a bit stupid. Maybe I should get a Myson, as the valve for the HW Santon tank is Myson and its manual lever is just spring loaded.
 
Sorry, just had a thought. There is a small black lever on the Drayton actuator head. It seems to be locked in place and I'm not sure how to move it without breaking it? I guess it's meant to be the manual override for filling? There's nothing in the instructions about what it does or how to move it. Sorry, I must sound a bit stupid. Maybe I should get a Myson, as the valve for the HW Santon tank is Myson and its manual lever is just spring loaded.

If it's has a and b on a label above it, leave that one

There's one other end of the wire, you will see a hole in the centre put a small screwdriver in there and pull away from the body, should pop out easy and move
 
Yes, thanks, but I can't see anything in the instructions about moving it. Do you only unlock it for filling the system? The existing one is in the lock position so I guess that is "normal operation"? Can you just remove the actuator and manually turn the spindle for filling? What's the lock for? Sorry to keep asking all these questions. Trying to help save my son some money. :)

I wonder if I should get a Myson, they are expensive but just have a lever which slides over and springs back. Thanks so much for all your help.
 
You could take the head off for filling the spindle should be lose and easy to move. As mentioned earlier about 20 degrees.
 
Yes, thanks, but I can't see anything in the instructions about moving it.

On page 2 of the installer's guide:

"When the manual lever is moved to the right and pushed in to ‘lock’, the valve is open, it automatically releases when the valve is powered."
 
Hi. All Sorted your help was much appreciated. Discovered the drain valve near the motorised valves so just drained - only about 2 litres came out, rest stayed in system. No problems repressurising and restarting boiler. Thanks again. Barry
 
Status
Not open for further replies.

Reply to Motorised valve allowing water flow even though spindle closed in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
127
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
244
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
184
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
277
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock