Hi All, I recently ran out of heating oil and consequently the Riello burner locked out. Once I was refuelled I bled the oil supply to the burner and after several attempts to reset, it kicked in, albeit with a whirring noise on startup. It has run for 3 days and I had noticed the whirring noise was still evident during the 3 days. Today the burner locked out again and I have bled the oil supply again in case there was still trapped air, and after several attempts the burner has kicked in. Please could I have some opinions on whether this now still to do with remaining air or could there more probably be other issues such as dirt in the system, and what I should investigate if it locks out again? Thanks.
 
Did you replace the main line oil filter/internal pump strainer/filter once refuelled before trying to restart?

There be lots of Rubbish/potential water at the bottom of empty oil tanks.

Rubbish could be restricting the oil pump or nozzle.

If the oil supply is being restricted some how, the burner will not have the oil/pressure to burn correctly at the current air settings. This could potentially result in an incorrect burn and dangerous gases being created.

You seem pretty handy and probably don’t wanna here this but please don’t start changing nozzles etc.
You really need to get an oil guy in to give it the once over and check combustion performance.
 

Reply to Oil burner locking out in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not...
Replies
1
Views
642
Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for...
Replies
19
Views
870
I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
788
Hi, we have Worcester Bosch heatslave external oil boiler 18/25 Boiler locked out. Pressure was below 0.5 so brought pressure back up. When lock...
Replies
2
Views
1K
Hi, I have had this problem for a week now. The oil boiler will run for a short while and then stop. If I check the pipes around the 3 way valve...
Replies
3
Views
848
Back
Top