becasue sometimes the trained and experienced eye will see things that the untrained dont. there is obviously a problem and if its fumes you need to get an oil engineer in

I'm not at all suggesting I wouldn't get an expert in. It's just that I've wasted money on two already. What I'm asking here is what could it be (what are all the options), not how I could identify which of the options it is. If no-one can even think of anything it reasonably could be then I'm reluctant to pay for an expert to just come round and confirm that he too doesn't know what the problem is. So far I've been able to rule out the options that people have suggested just by logic alone, unless I'm going to accept massive coincidence as part of the explanation (which at this rate I might have to, but not without a thorough investigation).

The burner must be perfectly level, the drip rate correct and the inlet totally clear of carbon deposits ( without widening or damaging the jet). Sometimes an ultra sound cleaning is needed

OK, I think I've done that, obviously my cleaning could be improved, but it's never been a problem before, so probably not this one.

The flame pattern on high should be even and totally blue, - when on low, the burner top should glow dull red.

Yep, flames totally blue, burner glowing red.

In your earlier post you referred to “the burner” popping - that is oil starvation - how did you correct that if the adjuster valves are rusted? - or have I miss understood.

Weird thing that. I took the burner out, scraped really well at the chamber lid, which still had a little carbon on it, made sure everything was really well seated, put it all back and no more popping. I can only presume that the small amount of carbon was enough, or maybe I'd not seated everything properly. Certainly odd, and I'm sure it's connected somehow, but it's not popped again since my first re-service.

Normally by taking time and thoroughly cleaning and methodically rebuilding the burner they work. Occasionally you get a burner that is level after setting up, heats unevenly and then distorts to being off level in use - that can cause poor combustion.

Interesting - would it go back to level again when cold? I've checked levels each time I've had the burner out and they've been OK each time. By OK I mean just like they always have been.

Are you sure that you have not cracked the cast iron part of the burner?

Can't be sure, but the seepage is not limited to one place, it's around the chamber lid and at the very top edge of the channels all around, so not like I would expect a crack to show.

What I do with two older (1970’s) ranges that I service (and are difficult / problematic to set up) is have a second burner set. So at service time, I clean the chamber and swop over the burners. I then refurb and clean the old burner in a workshop environment ready for the next service.

Good Idea. One of the solutions I'm thinking I might do is just buy a new burner and keep the old one a s a spare. Can I still buy burners, and do I need to worry about what size pipe it's connecting to, or are they all standard?

Sadly, with old ranges, they all have their own idiosyncrasies

So I'm finding. I just read on some other forum someone who had this smell for four years, despite servicing twice a year, they changed engineers and after the first service by the new engineer the smell went away. Apparently the engineer couldn't even say what he'd done!
 
Issac,

Do you you think there is any possibility that you have inadvertently disturbed the flue closure plate?

If you are getting a good blue flame picture, I would expect any minor seepage of oil at the burner to be drawn either for combustion or unburnt up into the flue. If the flue seal has been disturbed that may account for your smell.
 
Vapourising (unfortunately, given your area of expertise).
[automerge]1570688570[/automerge]
Just had the whole lot out again, re-fitted everything, changed wicks etc. Still the same smell. Seeing as there's some ambiguity I'll just clarify a few points.

It's a vapourising oil burner - two channels and a central chamber with a lid, wicks in the rings, large perforated rings sitting between the wicks. all this in a converted 1969 Rayburn Royale.

Most importantly (which seems to have been missed by a couple of respondents) the smell was completely absent the day before the service, then arrived (badly) the day I re-lit it. It's been serviced to a greater or lesser extent (we've tried different things each time) six times since. The smell got slightly better the first time, then it's stayed the same since. So without any further explanation as to why...

It's not the flue - how could the flue suddenly become blocked coincidentally on the same day I happened to be servicing it? (not only that, but I've tested it with lit newspaper and it draws fine)

It's not the seals - I could have put things back wrong once, but all six further occasions with two of them not even me doing it, especially when no such thing has happened on the previous 12 times I've serviced it. Again, if the seals are at fault it would have to be an astonishing coincidence.

It's not oil the levels - the adjusters on both the oil control valve and the burner are completely rusted, the relative levels are exactly the same as they've been (probably for the last 20 years!). I've also checked and timed the oil supply rate.

It's not the wicks - I've changed them to no effect.

It's not the oil itself - Same as the others, it was fine the day before the service, bad after. Same oil.

It's not the rings or the chamber lid - I've checked both are seated completely flush and down to bare metal where they meet. Also, again, the same procedure I've done twelves times in the past and now got wrong six times times in a row, doesn't make sense.

It's not leaking oil anywhere - I've had paper towels down, as advised, around the whole burner unit and pipework for nearly an hour with it full (but unlit). Not a drop of oil anywhere but inside the burner itself.

The only thing that I noticed during this last test, it that the oil kind of wicked outside of the chamber and channels of it's own accord. Just like if you made a cup out of paper, oil would sort of wick up the sides beyond the fill level. That's what the oil was doing, it was like the burner was made of paper (rather than cast iron) and the oil was sort of 'seeping' through it. Just a little bit so that the i could see a damp mark on the outer edge. I don't know if this is normal, however, nor do I have the faintest idea what might cause it that would tie in with the fact that this happened after a service.

I'd be really grateful for any ideas, but please don't just suggest I get an engineer in. I may well do so, but there are a finite number of things that can go wrong, with a finite number of causes. If none of the experts here can even suggest something that might actually cause this problem (given the history I've outlined above) then why would an engineer who comes to see it suddenly be able to think of something? I just need some ideas, even if I just pass them on to an expert I employ to fix them for me.
Sorry i presumed it was a pressure jet burner . I’m 54 an d haven’t done many vaporising burners.
these are tricky to set up and are done with mostly the naked eye. And a second sense of flame picture.
i would advise you get an older engineer to come and service your boiler .ask them if they have good experience in vaporising burners. apart from aga’s they can’t be many left!
 
Do you you think there is any possibility that you have inadvertently disturbed the flue closure plate?

Yes, It's not impossible, however...

The problem has inexplicably been fixed. After my last take-everything-out-and-put-it-back-again the smell persisted for about half a day, i turned the dial up a fraction (just to get our hot water back) and the smell went away, 24hrs later it's still gone. I should say, in the previous couple of weeks wrestling with this problem I have tried all sorts of settings so it's not just a matter of higher flame=no smell, it must additionally be something I did last time.

Anyway, I haven't dared try it on any other settings yet (I just want a break from fixing it for a while), but there's one matter I'd like to ask your opinion on, if it's OK. All this recent fixing issue has made me hyper-attentive to flame colour and now I'm not trusting my memory of what it's normally like. I've had 100% blue, but sometimes I look and there's a trace of yellow/orange, just at the tip of the otherwise blue flames. I'll try to get a photo, but it looks just like this image from the guidance I've been using.
aga8.jpg

not literally 100% blue. Is that something I need to get checked out, or is that part of what you'd still call 'blue flame'?
 
Issac,

The flame should be completely blue. The yellow flicker is sign of incomplete combustion - which could just be dirt in the burner.

I would source a second burner set and next time you service the range swop out the burners and give the existing ones a thorough clean and check for cracks and / or porosity in the cast iron.

Having said all the above - the yellow flicker you have at the moment is not a major issue - but it will increase the volume of carbon deposit / sooting.

It may settle down after a few days.

Good luck
 
Issac,

The flame should be completely blue. The yellow flicker is sign of incomplete combustion - which could just be dirt in the burner.

I would source a second burner set and next time you service the range swop out the burners and give the existing ones a thorough clean and check for cracks and / or porosity in the cast iron.

Having said all the above - the yellow flicker you have at the moment is not a major issue - but it will increase the volume of carbon deposit / sooting.

It may settle down after a few days.

Good luck

Thanks.

Unfortunately the smell has just come back again. I haven't done anything except open the top door (I was thinking of getting a photo of the flames), literally haven't touched anything - how's that even possible?

The only thing I can think of was that it was really windy the 24hrs over which there was no smell. So maybe all that was happening was the smell was being drawn up the flue better (as I think you've mentioned should happen). I suppose that might indicate something wrong with the flue (so I've booked to have it swept anyway - just in case), but I think it unlikely because I can't see how it would suddenly become a problem overnight. If you remember, this problem was non-existent the day before the service and the arrived the day after. Can a flue block up that quickly?

One weird thing I'd like to ask an expert. In our flue box, the exit from the Rayburn itself is blocked by two sheets of metal with a 1-2cm slot cut in one of them - meaning the entire exit hole is narrowed to about 1x5cm. It's always been like this and I presumed it was something to do with the conversion to oil (the Royale is a solid fuel range really). The reason I ask is that if 1x5cm is the correct exit hole, then it's very hard to see how any flue blockage could possibly result in a draw less than that (the flue is about 10cm diameter), but if it's not normal, then I suppose all sorts of things might have gone wrong with it? Why might the flue exit need to be narrowed in the first place?
 
Issac,

Starting with the restrictor plate in the flue. This is normally a plate that slides across the bottom of the flue inlet to optimise the “pull” from the flue on the boiler. The pull on the flue ( if you can measure it ) for a vaporising burner should be less than -1 mm H2O but not more than -1.5mm H2O. The plate you describe has probably been custom made to give those conditions rather than adjusting the restrictor plate. That is not unusual - it is a one time setting normally.

I assume that when you had the “engineers” out they measured the boiler draught? You cannot do that yourself - unless you have the equipment!
What you can do is:

For the flue, check for spillage using a match test all around the spigot, joints and restrictor (if fitted).

Check all the door seals on the range - thay must all be tight fitting and not pass air in either direction.

Check that the room ventilation providing the combustion air is properly sized for the boiler. The boiler should run properly with all doors and windows closed any extract fans switched off, so that all combustion air is only coming through the permanent vents.

Also may be worth rechecking that the burner shells are all undamaged and seated properly - they should be a tight fit into the burner to be as airtight as possible.

Apologies, I have no real immediate advice - I think that you now just need to work through the complete basic set up of the range to ensure that it is all correctly configured. I appreciate that you probably do not need it, but the starting point is always a flue clean
 
Starting with the restrictor plate in the flue. This is normally a plate that slides across the bottom of the flue inlet to optimise the “pull” from the flue on the boiler. The pull on the flue ( if you can measure it ) for a vaporising burner should be less than -1 mm H2O but not more than -1.5mm H2O. The plate you describe has probably been custom made to give those conditions rather than adjusting the restrictor plate. That is not unusual - it is a one time setting normally.

Thanks. I've had that plate out, cleaned it and put it back several times during services as I always check the flue box as part of my service. I've never been particularly accurate in how I put it back (not to the mm type accuracy) so it's in basically the same place it's always been. One less potential cause I think.

I assume that when you had the “engineers” out they measured the boiler draught? You cannot do that yourself - unless you have the equipment!

I wasn't in the room with them all the time, but I don't think they did anything like that. They didn't mention it anyway. They just took the burner out, scraped it a bit, put fresh wicks in (I think), vacuumed around the chamber and fluebox and that was that. As far as I know. I clearly need to get myself some more technical engineers.

For the flue, check for spillage using a match test all around the spigot, joints and restrictor (if fitted).

Done. Match was steady all around, good draw in through the air inlet. There's no sign of any actual draught, even from the hob and chamber door where the smell is coming from.

Check all the door seals on the range - thay must all be tight fitting and not pass air in either direction.

The hob seal is new(ish), the burner chamber door doesn't have a seal and never has had. There's not even a place for one to go as far as I can tell.

Also may be worth rechecking that the burner shells are all undamaged and seated properly - they should be a tight fit into the burner to be as airtight as possible.

Done. Measured them with a flat-plate. They're completely flat at the base. The engineer mentioned possibly using exhaust sealant paste if the problem continued, but I'm reluctant to do that as it's obviously never needed it in the past.

Apologies, I have no real immediate advice - I think that you now just need to work through the complete basic set up of the range to ensure that it is all correctly configured. I appreciate that you probably do not need it, but the starting point is always a flue clean

Not at all, you've been really helpful, I greatly appreciate it. The flue clean is booked in (over a month off though, our sweep is very popular at this time of year), so I'll just have to wait for that and go from there.

Thanks again for your help.
 
Thanks,

Very helpful responses.

Firstly, don’t be tempted to use exhaust paste on the burner shells - they are virtually impossible to clean properly after it has been applied.

I don’t normally like to propose trial and error solutions - but it may be worth trying the range without the restrictor plate in place, or if you can with it partially removed.
 

Reply to Oil fired Rayburn persistent fumes after service. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, I have a wallstar combi oil fired boiler. We got low on oil a couple of weeks ago but didn't run out. Since we've had our oil delivered...
Replies
6
Views
661
Hi, Newbie here so feel free to teach me the etiquette of this place, and apologies for the lengthy opening post. The boiler started locking out...
Replies
4
Views
735
Hi we had a recent service on our 40 year old Thorn oil boiler, we fire it up for the 1st time since the service todayfor got water, after 20...
Replies
2
Views
1K
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer...
Replies
3
Views
580
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock